Heated floor issues

Hello I am trying to wire up a heated floor, all of the tiles and everything are already done and the wires are sticking out of the wall ready to be wired up. Before I went any further I consulted AI to make sure everything works before I go any further. After several tests with a multimeter a potential issue came up. There are two power wires and one ground shield braid and then two sensor wires. Testing ohms from each power wire to ground it’s supposed to read OL but when I tested them on the 2k setting I got .002 black to ground and .04 yellow to braid. Does this mean there is a ground fault happening somewhere or the wire is damaged somewhere? Or is it fine?

1 Upvotes

13 comments sorted by

•

u/AutoModerator 2d ago

Attention!

It is always best to get a qualified electrician to perform any electrical work you may need. With that said, you may ask this community various electrical questions. Please be cautious of any information you may receive in this subreddit. This subreddit and its users are not responsible for any electrical work you perform. Users that have a 'Verified Electrician' flair have uploaded their qualified electrical worker credentials to the mods.

If you comment on this post please only post accurate information to the best of your knowledge. If advice given is thought to be dangerous, you may be permanently banned. There are no obligations for the mods to give warnings or temporary bans. IF YOU ARE NOT A QUALIFIED ELECTRICIAN, you should exercise extreme caution when commenting.

I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.

1

u/WedgeOfLettuce 2d ago

Update: I’ve discovered a small nick in the blue heating wire right before it goes under the tile, would this be the reason for the wonky numbers?

1

u/SlightlyFlustered 2d ago

Chances are you are just seeing the outside damage and the wire has been crushed so that the shield is shorted to a power wire.

1

u/Eyedea777777 2d ago

Are you getting continuity between the power wires and ground? If not its fine

1

u/WedgeOfLettuce 2d ago

Ya there is continuity between the powers and ground :(

1

u/LaufSeiglaRaceE1 2d ago

So if you put the meter in continuity buzzer and touch one lead to hot and one to ground, it beeps?

1

u/WedgeOfLettuce 2d ago

Yes, yellow to ground beeps and reads 40 ohms and black to ground beeps and reads 2 ohms

1

u/LaufSeiglaRaceE1 2d ago

.002 is next to nothing. Probably just resistance of the wire run itself.

1

u/SlightlyFlustered 2d ago

Or even the meter leads.

OP what does the meter read with the leads touched together.

1

u/WedgeOfLettuce 2d ago

It reads .000 with probes touching

1

u/SlightlyFlustered 2d ago edited 2d ago

Actually that makes sense for 2k range. Try a lower range. 0.04 is 40 ohms.

The current draw at 120V with a 40-ohm load is 3 amps (which equals 360 watts of power). Possible for a large bathroom. 10 - 15W sq/ft perhaps. 24 - 36 sq feet.

The 2 ohms to ground is not ok though.

1

u/Flat-Barracuda1268 2d ago

A power wire connected to the shield is an issue. Wire likely got damaged during the tile install. Sorry, that sucks.

1

u/rustbucket_enjoyer Verified Electrician 2d ago

Game over