r/AusElectricians • u/brainfractal • 5d ago
General Parallel mains formation question
Which formation is correct, or are both okay.
Im running 240mm parallel mains and know you change the order between bundles because of emf and all that, just not sure if both are okay or only one option is
Cheers in advance legends
9
Upvotes
51
u/electron_shepherd12 ⚡️Verified Sparky ⚡️ 5d ago
Here’s the recommended configurations that are in the back of AS3008.1.1
16
u/Ok_Currency8525 5d ago
Look in AS3000 it’s in there. Make sure cables are all exact same length aswell.
9
u/rafffen 5d ago
You want same colour phases facing each other, helps reducing emf magic bullshit
1
u/Kruxx85 5d ago
Both are correct - idea is lay them out equally, then swap two cores.
Which you have. Option 1 is WB swapped, Option 2 is RB swapped
3
u/mario_ninja 5d ago
I prefer option 2. Always keep white on top. Check where its being glanded and terminated to see if they will go in nicely. Should only need to rotate one trefoil.
2
u/Boony79 4d ago
First time ever posting a comment on Reddit but finally found something I could contribute on.
Option 1 (asymmetrical) but 3008.1.1 says should be adopted, not must (unless they’ve updated the latest revision. Need to get my hands on it..
It’s done this way because it an symetrical arrangement in trefoil can:
Bottom of the line. Do it as per option 1 unless you’ve addressed all 3. Especially number 2. Bit me hard once.
1
u/Perth_not_now 5d ago
As long as the field of each bundle rotates in opposite directions. Option 1 is my go to but both are correct.
-5
u/toddlerpunter 5d ago
How long is the run ? Over short runs it really wouldn’t matter all that much.
-8
u/SchulzyAus 🔋 Apprentice 🔋 5d ago
RR WW