General Parallel mains formation question

Post image

Which formation is correct, or are both okay.

Im running 240mm parallel mains and know you change the order between bundles because of emf and all that, just not sure if both are okay or only one option is

Cheers in advance legends

9 Upvotes

19 comments sorted by

51

u/electron_shepherd12 ⚡️Verified Sparky ⚡️ 5d ago

Here’s the recommended configurations that are in the back of AS3008.1.1

4

u/Electrical-Flan-102 4d ago

Pleb here. What happens if you don't follow that?

9

u/shmooshmoocher69 4d ago

1, 2 Eddies gonna get you

1

u/HydraAUS 3d ago

An he won’t buy you dinner first

16

u/Ok_Currency8525 5d ago

Look in AS3000 it’s in there. Make sure cables are all exact same length aswell.

5

u/NothingVerySpecific 5d ago edited 5d ago

Make sure cables are all exact same length aswell.

absolutely the legal requirement as stated... but pragmatically it annoyes me.

isolation issues aside, if one feed is a bit shorter, it has less resistance so it takes more of the current, so it gets hotter, so resistance increases, so it takes less of the current & the whole system becomes stable.

this is fundamentally why UK ring circuits work just fine. the whole isolation issue seems like hand waving. I would have been dead before my apprenticeship ended if I didn't always test for voltage before touching.

someone make it make sense. did the code just forget second & third order effects?

(edit: I'm not disagreeing with you, or the legal requirement. I'm just trying to understand if I'm missing something obvious about the theory. my 'vibe' is 30% difference in length shouldn't make a bit of difference)

2

u/hannahranga 4d ago

absolutely the legal requirement as stated... but pragmatically it annoyes me.

It annoys me too, we're sparkies not machinists they're going to follow the same route and not have one off random extra loops hiding in a pit sure but that's still going to have a fairly generous tolerance. Imagine laying all the cores out first to cut them the same within 0.1mm, pulling them and then the apprentice fucks the termination on the last one.

1

u/Intumescent88 3d ago

I guess they're trying to avoid melted cables.

Similar occurs with parallel runs of differing CSA. Say you run a parallel of 2.5 and 4mm. Guess which one melts first?

It's the larger cable. 😐

0

u/eliitedisowned 5d ago

If I'm doing cable calcs I'll have 10% minimum spare capacity from full load current. If there is long runs then the voltage drop is deciding factor for cable sizing and they will have way more spare capacity.

Would love to model it one day and see how much changes in current across conductors if one is slightly shorter/longer.

9

u/rafffen 5d ago

You want same colour phases facing each other, helps reducing emf magic bullshit

1

u/Kruxx85 5d ago

Both are correct - idea is lay them out equally, then swap two cores.

Which you have. Option 1 is WB swapped, Option 2 is RB swapped

1

u/brainfractal 5d ago

Thats where im confused tbh, i wasnt sure if the idea was that the cores are mirrored so that does the trick making it safer or if swapping 2 cores is what does the trick regardless of mirroring

1

u/Intumescent88 3d ago

It's just phase rotation, same as any 3 phase application. Swap any 2 cores and you have changed rotation.

3

u/mario_ninja 5d ago

I prefer option 2. Always keep white on top. Check where its being glanded and terminated to see if they will go in nicely. Should only need to rotate one trefoil.

2

u/Boony79 4d ago

First time ever posting a comment on Reddit but finally found something I could contribute on.

Option 1 (asymmetrical) but 3008.1.1 says should be adopted, not must (unless they’ve updated the latest revision. Need to get my hands on it..

It’s done this way because it an symetrical arrangement in trefoil can:

  1. Cause additional mechanical stress’s under fault conditions
  2. Cause imbalance on current distribution despite identical cable lengths
  3. Induce voltages into metallic wiring enclosure that cause heat and potentially damage cable insulation

Bottom of the line. Do it as per option 1 unless you’ve addressed all 3. Especially number 2. Bit me hard once.

1

u/Perth_not_now 5d ago

As long as the field of each bundle rotates in opposite directions. Option 1 is my go to but both are correct.

-5

u/toddlerpunter 5d ago

How long is the run ? Over short runs it really wouldn’t matter all that much. 

-8

u/SchulzyAus 🔋 Apprentice 🔋 5d ago
BB

RR WW