Occupied Setpoints vs regular setpoints

Hi guys, What is the difference between occupied cooling/heating setpoint and a regular temp setpoint?

1 Upvotes

13 comments sorted by

9

u/Congie91 15h ago

Probably talking about a setback setpoint vs occupied setpoint?

Setback is for when the system is still required to run but no one’s using the space. To prevent conditions completely being lost you set a setback setpoint that helps maintain temperature but save energy use.

2

u/Exoticcollects 15h ago

Ahh ok thanks bro

6

u/DirtGotNo 10h ago

think I understand what you’re asking. I didn’t fully understand it at first either.

The occupied heating and cooling setpoints essentially establish the deadband. For example, if occupied cooling is 72 and occupied heating is 69, that’s a 3-degree deadband.

The zone setpoint comes into play because it shifts those heating and cooling setpoints up or down while maintaining that deadband. The controller uses the effective heating and cooling setpoints to determine when heating or cooling is needed.

You can also effectively bypass the normal operation of the zone setpoint by drastically adjusting the occupied setpoints. For example, raising the occupied cooling setpoint or lowering the occupied heating setpoint far enough can prevent the controller from calling for cooling or heating, even though the zone setpoint hasn’t changed.

The zone setpoint still factors into the calculation, but changing the occupied setpoints can alter how the controller responds.

1

u/Exoticcollects 5h ago

Thank you for this, that clarifies a lot. Now regarding the actual change between heating and cooling mode, typically what would allow the controller to make that adjustment? Im assuming it would be a OAT point or zone temp point correct?

1

u/DirtGotNo 5h ago

In a VAV application the actual ZN-T would make the controller change between HTG & CLG. For example If your effective CLG SETPOINT is 68 the box will go into cooling mode when the ZN-T goes below 68

1

u/Exoticcollects 5h ago

Wouldn't it be above 68?

2

u/DirtGotNo 4h ago

Yes sorry said it backwards

2

u/ScottSammarco Technical Trainer (Niagara4 included) 14h ago

Regular setpoint isn’t really a thing?

I suppose we could rename that “active setpoint “

There’s also single setpoint and dual setpoint control that are most common. I’d recommend doing research on those and learning more about typical setpoint control.

2

u/JustAnotherTrickyDay 9h ago

Also, if there's an occupied set point, there's usually an unoccupied set point. So your occupied set points might be 69/72, and then for evenings and weekends, the unoccupied set points might be 60/85 (school buildings for instance). Also, in occupied mode, the fans would be running. But in unoccupied mode, they would only activate if temps dropped below 60 or above 85.