r/BuildingCodes • u/Nine-Fingers1996 Residential Contractor • 6d ago
Fire wall
Is this fire wall properly built? Specifically the drywall isn’t continuous behind the ceiling track. Multi story concrete structure that was turned into condominiums. Unit I’m in had 2 layers 5/8” uninterrupted, fire caulked top and bottom. Located in MA.
2
Upvotes
10
u/This_dumpsterfire Building Official 6d ago
Fire wall, fire partition, fire barrier. This is not a fire wall. We wouldn't know for sure without the listed assembly.
4
u/IHerebyDemandtoPost 6d ago
Then no.
Firewalls must be continuous from foundation to roof.
There is only one exception for podium buildings.
2
u/picklesuitpauly 6d ago
Find the listing they used, bet it has to be continuous. Also we don't allow romex in steel studs even with bushings.
1
u/Novus20 6d ago
Why would they not run the wall right up to the underside of the concrete floor…….JFC
1
u/RuskiGrunt 5d ago
No I doubt it. Look at the plans the assembly is more likely to be called out as a fire barrier or fire partition instead of a fire wall for walls separating units. Fire Walls in multifamily construction are more serious and they divide buildings as a whole to reset travel distances on bigger buildings. That drywall doesn't even look like its 5/8". Obviously the wall is not completed. The outlet box does not have puddy pads on it. I am also not sure what the insulation is there for, just for soundproofing? Is that mineral wool or fiberglass?
0
u/GenConfusion 6d ago
why would you need a firewall in a concrete structure to begin with unless it's separating it from a wood structure?