r/DIYHeatPumps • • 14h ago

I decided to install a mini split myself after getting a $4,000 quote

Post image
165 Upvotes

I wanted to add AC to one of the rooms in my house, but the installation quotes were much higher than I expected. One contractor quoted me around $4,000, which felt like a lot.

I decided to handle the installation myself, and the equipment and materials came to about $1,200 in total. Before getting started, I spent some time watching installation videos and reading through the instructions. Eventually, I got everything set up. Looking back, I'm glad I didn't jump on that first quote.


r/DIYHeatPumps • • 4h ago

Supplemental mini-split

2 Upvotes

We converted from swamp cooler to Refrigerated A/C last year, and we are having an issue. We have one part of our house that doesn't heat/cool enough.

It seems the return vents are set up for swamp coolers and not A/C, and the air doesn't re-cycle properly. because of the way our house is set up, (cathedral ceilings) we can't move the return vents.

So, the idea is to install a mini-split/heat pump setup on that side of the house, about 600sft

Since the A/C is being used to supplement the house A/C, and not stand-alone, what size do I need? would I still use the 600sft measure? or something less?


r/DIYHeatPumps • • 1h ago

Large detached garage in southern NH

Post image
1 Upvotes

Looking for recommendations (specifically deals this week, if possible) and anecdotal data from those with similar setups. Closing on the house next week, and getting the garage up to a workable state is the first goal.

As the title alluded to; 45'x45' detached garage. It's currently uninsulated, but I will be doing Rockwool throughout most likely. Hopefully R21 or more on the walls, and as much as I can get on the rafters (primarily vaulted ceiling from ~10ft sidewalls up to about ~16ft in the middle). Rough mockup attached.

I primarily want to heat the larger open area for now, which is 45x32.

I don't need it to be 70F when it's -5F outside. Maintaining 50F on the worst case days is fine. I have a 18k Senville Aura in the current 24x36x14 shop and it has been absolutely perfect. It will easily freeze me out of it in the summer, and doesn't seem to struggle at all to maintain workshop comfort in the worst of the winter.

So, I guess what I'm looking for is:

  1. Sizing and placement, considering that it's not a house
  2. Specific models/deals this week that are worth getting this week.

r/DIYHeatPumps • • 1d ago

Mini Stat recommendations?

2 Upvotes

I have three Mr Cool mini splits I've been running for a few years. They work great but the temperature has always been a bit inconsistent when it comes to heating larger rooms. Follow me mode on the remote helps considerably but the way the wall bracket holds the remote, the IR sensor faces the wrong way which greatly impacts line of sight and where I can mount it (a really dumb design).

So I got some mini stats to replace the remotes. They're older ones, the Bluetooth only ones. But already seeing an improvement in heating larger spaces.

So, now that I'm using them, does anyone have any tips or tricks they've found useful? There isn't a follow me function on these so I'm assuming they auto do that. Is that right?


r/DIYHeatPumps • • 1d ago

how to think about heat pumps when you have nat gas heat?

11 Upvotes

Looking for ductless minisplit AC / heat pump.

My situation:

  • winter temps can dip into the low teens in my part of NY state. Doesn't really get lower than this.
  • have nat gas powered boiler and baseboard heat, and I'm in NY, so electricity costs are high (~$0.26/kWh), so using the boiler is more economically efficient even though not more energy efficient
  • BUT, I have solar panels and produce a bit more power than my spring/autumn/winter baseline usage since no AC for 9-10 months of the year, so while purchased nat gas is more economically efficient than purchased electricity, free electricity is best. And I figure using a heat pump can lower my high nat gas bills in winter.
  • this heat pump is for a home office. If it can handle heating even on the coldest days (low teens), then I can set the baseboard heat thermostat for the entire zone (of which the office is just a small part) to bare minimum to ensure baseboard pipes along perimeter walls don't freeze.

Given the low teens winter temps, it would seem the 5*F models would be fine, but these don't seem much less expensive than models rated for -13*F or even -22*F. Does it make sense to consider these -13*F or -22*F models even though I'll never see those temps?


r/DIYHeatPumps • • 2d ago

PSA: the current budget king at all time low on Amazon

30 Upvotes

I put one of these in like a month ago and have been very impressed at $600… at $479 it’s unbeatable. The rovsun 9k 23 seer unit is based on the next generation TCL T pro r454b system, AHRI certified and NEEP ASHP tested down to -13f, extremely quiet and compact / low profile. I’m running mine 100% off grid with solar and it sips power, usually sits between 350w and 600w unless I’m rapidly heating a space. Retains most of its output at 5f at COP over 2, there are almost no other options in the sub-1k category that put up heating specs like this. HSPF2 Region IV is 10. Amazon link matches the tracked all time low and hasn’t been that low in a long time.

This is not an ad, I bought it for $600 - just sharing for folks looking to do something soon. Tempted to buy another just to have even though I don’t have a spot for it lol


r/DIYHeatPumps • • 3d ago

Mini split for South Central Alaska

4 Upvotes

I building a small (768 Sqft) house in the Kenai area. I really want to do a mini split for my primary heating, with Propane backup. The house will 2 bedroom and an open Kitchen living room. Bedroom 1 is about 150 SQ Ft, Bedroom 2 is about 100 Sq Ft and about 200 Sq ft for the Living\kitchen. I was thinking a 3 zone unit. One in each bedroom and one in the living\kitchen. I really like the Senville Aura. I was thinking 6k in each bedroom and 9k in the living\kitchen. I building the house to be very energy efficient. Air sealing, continuous insulation, High R value .

Is the 2 6k and 1 9k enough or should I do 9k and 12k? Also any other brands I should look at. I will be doing the work myself and my Father is a licensed HVAC Tech and he will help me if I need it.


r/DIYHeatPumps • • 3d ago

Albott DIY series: Easiest mini split install No vacuum, electrician, or HVAC tech required!

Thumbnail
youtu.be
20 Upvotes

I installed my first and second mini split and although I'm sure I could have bought a cheaper unit that didn't have the quick connect line set, this is much cheaper than a Mr. Cool and the warranty does not require professional installation. This is a major step in my ability to go off grid.


r/DIYHeatPumps • • 5d ago

Would you be concerned about a mini split mounted this high above a garage?

5 Upvotes

This is a Costway Blast Pro Series outdoor unit mounted on the wall above a garage door. The height is what caught my attention. It keeps the unit off the driveway and out of the way, but getting up there for cleaning or maintenance doesn't look particularly convenient. I've been looking into a mini split AC for garage as part of a home workshop setup, and I'm trying to understand the tradeoffs of mounting the outdoor unit this high.

Would you be more concerned about access for servicing, vibration through the wall, or clearance around the unit? I like that it doesn't take up any floor space, but I'm not sure I'd choose this location without checking those things first.


r/DIYHeatPumps • • 5d ago

MRCOOL MRCOOL Low Fan When Heating

1 Upvotes

I have a MRCOOL hyper heat 2nd generation unit that I installed earlier this year. So far, cooling over the summer and heating over these few weeks has been good.

I ran into an issue this evening where my thermostat was schedule to go to 70F at 6pm. I got home around 6:30 and the indoor and outdoor unit seemed to be running in a very low fan mode.

I tried stopping and starting the system from the thermostat, it seemed to go through a defrost cycle and then I got the same behavior.

I had to turn it off and turn it back to heat at the thermostat for it to start working properly again. I had this happen one other morning as well.

For what it’s worth, my indoor unit shows “LO” on the control board display. The manual does not list this as a display code.

Can anyone explain why my unit was behaving this way and what “LO” means?

Edit: I called MRCOOL and LO is actually “07”, I have a down flow config so my unit is upside down. The MRCOOL tech I talked to couldn’t definitely say why my unit was behaving this way, but I agreed to monitor it and will call them back if it happens again.


r/DIYHeatPumps • • 6d ago

Very slow pressure test drop...

Post image
2 Upvotes

tldr; my pressure test very slowly dropped from 455psi to 425psi over about 20 hours...

It feels like I am chasing a gnat.

New installation of a 2-zone Pioneer minisplit. Pressurized one zone yesterday late afternoon and it looked good. But today it has dropped enough that I can't ignore it. ~30 psi down over about 20 hours. But when I spray with BigBlu, I am not finding anything - it seems too small of a leak to show up at the moment.

Anyone have any suggestions on how to chase this down?


r/DIYHeatPumps • • 6d ago

Heat pumps vs gas/oil furnace heating cost comparison

5 Upvotes

All calculations were done by hand.

TL;DR:

Heat pumps and gas furnace save 50%+ on heating compare to oil furnace at new england area.

Saw a similar topic post last week but it was AI slop so I decided to go down into the rabbit hole, after some brief calculation I realized the cost is heavily depends on the climate, $/kWh, gas and heating oil prices. So instead of a fixed price, I made a benchmark in terms of heating price and hopefully this can give a concept how much you can save from heat pumps. Compare to the benchmark, the lower your $/kWh is, the higher your heating oil and gas price, the more efficient your heat pump, the more you can save from switch to heat pumps.

Reference price - based on new england area average price, simplified for calculation:

Heating oil $6/gallon, electricity $0.25/kWh, natural gas $2/therm

Oil Furnace - baseline

5-10 years old, medium condition, 72% efficiency (80% burning efficiency, 10% ducted loss):

One gallon of No. 2 heating oil can provide 99,720 BTU = $6

Gas Furnace:

5-10 years old, medium condition, 76.5% efficiency (85% burning efficiency, 10% ducted loss)

For same amount of BTU need 1.3 therm NG ≈ $2.6

New installed, condensed gas furnace, 85.5% efficiency (95% burning efficiency, 10% ducted loss)

For same amount of BTU need 1.17 therm NG ≈ $2.33

Heat Pumps - Mitsubishi M series, ductless but well-represent ducted heat pumps efficiency, 10% ducted loss:

For same amoung of BTU

COP2.0@5F - ducted: 16.24Kwh ≈ $4.06, ductless: 14.61Kwh ≈ $3.65

COP2.64@17F - ducted: 12.3Kwh ≈ $3.07, ductless: 11.07Kwh ≈ $2.77

COP3.84@47F - ducted: 8.45Kwh ≈ $2.11, ductless: 7.61Kwh ≈ $1.9

Annual heating cost example:

Take a new england family house as an example, according to EIA, average new england US family use about 600 gallons per year, so the total cost of heating oil is $3,600.

For same amount of BTU, gas furnace will need about 782 themal NG ≈ $1,564, save 56.5% compare to oil.

As for heat pump, assume 10% BTU needed at 5F, 15% BTU needed at 5F - 17F, 75% BTU needed at 17F - 47F (again, oversimplified model for new england area, COP are variable between 17F-47F, by using COP@47F offset the higher efficient zone when above 47F)

COP2.0@5F - ducted: 974Kwh ≈ $243.55, ductless: 876.79Kwh ≈ $219.2

COP2.64@17F - ducted: 1107Kwh ≈ $276.75, ductless: 996.35Kwh ≈ $249.09

COP3.84@47F - ducted: 3805.5Kwh ≈ $951.38, ductless: 3,424.95Kwh ≈ $856.24

Heat pump total cost:

Ducted: $243.55 + $276.75 + $951.38 = $1,471.68, save 59.12% compare to oil.

Ductless: $219.2 + $249.09 + $856.24 = $1,324.53, save 63.2% compare to oil.

Hints for choosing cold climate heat pumps:

Beware of the heating capacity at your local coldest day, better check the NEEP list before you purchase. One thing I noticed is that the min operating temperature and the max heating btu are different stories.

E.g a mini split can rated 12k btu and able to run at -22F, but doens't means it can provide 12k btu at -22F.

Different manufacturers disclosed it differently, but NONE of them mentioned the heating btu at min operating temerature on their product pages. By far I've only spotted Della said their cold climate units can maintain 100% heating btu at 5F, and Zone air said their DIY series can maintain 85% heating btu at 5F, thats all. I think this is where the impressions of heat pumps aren't working well in cold climate came from, you're getting way less heating btu at lowest operating temperature. All brands that I research have neither COP curve nor max heating btu at lowest operating temperature.


r/DIYHeatPumps • • 7d ago

Quick connect Mrcool

4 Upvotes

Can someone who has used MrCool quick connect lineset provide their input on the reliability of this option. I don't know if I should try this or a smart fitting with regular pipe and vacuum and charge.


r/DIYHeatPumps • • 7d ago

BTU cooling for 36x60 shop

Thumbnail
gallery
3 Upvotes

I have a 36x60x14 pole barn that has 2 inch closed cell spray foam on walls and ceiling. 2 Insulated doors overhead doors 2 windows. I consider it very tight. I’m wanting to install a mini split single head got a quote from a company that started out at 3 tons but said a 2 ton would likely work just might not keep up when it’s 100 degrees out. Live in central Iowa does anyone have a similar shop that they have a mini split or any advice would be great. When you jump to 36k from 24k the price goes up a Decent amount. Going to probably go with a Della brand and rent there tools to get warranty. Quote I got was 6k to install.


r/DIYHeatPumps • • 7d ago

mr cool central ducted hyper heat leaking oil at air handler quick connect fitting

5 Upvotes

I recently installed a 24k central ducted hyper heat and it's been running great for the past week.

However, I just went up to attic and noticed some oil staining under the larger diameter line set right at the air handler connection point.

I'm wondering if I over or under torqued it (should I have bought the torque wrench). Is it possible to turn off unit, close the valve using the allen key, then disconnect the 3/4 line set, and then the quick connect adapter thing (which I think it's leaking from).

I'm just wanting to confirm refrigerant won't pour out with this method.


r/DIYHeatPumps • • 8d ago

Overwhelmed by Mini Split options

9 Upvotes

I am a landlord with 800 sqft apartments and updating the units from 30+ year old swamp coolers. Climate is up to 110 in the summer and down to single digits in the winter. The units also have wall heaters and wood burning stoves.

From what I can tell, mini split is the best option, but there are an overwhelming amount. It is a remote area, and I’d like to order one for pick up from the closest Home Depot, and or use someone with relabel shipping.

Is spending under 1,000$ realistic?

Thank you!


r/DIYHeatPumps • • 8d ago

MRCOOL MrCool 18k 5th gen heating good (so far) at 34 degrees outside 😅

Thumbnail
gallery
50 Upvotes

r/DIYHeatPumps • • 8d ago

How DIY friendly are they?

2 Upvotes

Has anyone (non hvac tech) here done a full install that required brazing and line charging?

I installed my system and now am having an issue getting someone to charge it. It’ll required flare-braze to connect lineset then additional refrigerant . I had a couple people lined up who seemed to have ghosted me and not sure what to do next.

I’m pretty handy but don’t have nitrogen, b-tank, refrigerant, gauges let alone know how to use them.

Any suggestions?


r/DIYHeatPumps • • 10d ago

What are some of the prerequisite skills for a DIY heat pump install?

17 Upvotes

I'm no stranger to DIY and I've got a garage full of tools, including a vacuum, pump and micron gauge as well as gauges for 410a. My home's HVAC is all professionally installed, but I wanted to add a heat pump ductless to my detached garage and figured the units are cheap enough to warrant giving it a shot. I can run the electrical, no stranger to gauges, mounting the units definitely won't be an issue. Where I'm not sure is running the linesets and possibly bending them. Am I being overly cautious here?


r/DIYHeatPumps • • 10d ago

PSA - Please use a micron gauge, do not cheap out.

25 Upvotes

Someone was telling me the other day they were using a manifold and vacuuming to -30 or whatever because a micron gauge was too expensive.

Here is a perfect example.. this is a $350 gauge for $60+ shipping. I have zero affiliation with this listing, it is not an advertisement. I do own this same gauge though and it works great. Sometimes with used micron gauges you have to clean them with alcohol... but thats not difficult. I see used yellowjackets and fieldpieces pop up often on eBay.

Please do not install any system without using a micron gauge. You are almost guaranteed to leave moisture in your system which will significantly increase the risk of early compressor failure.

For a cheap VCRT, the Hongsen/Elitech VCRT is under $20 and holds a good vacuum.

EDIT - Wow, did not realize this sub was full of a bunch of hacks who try to justify doing half ass work. As someone who actually has experience working in HVAC.. let me tell you something. Pulling a vacuum blind without a micron gauge for several hours is NOT a solution. Doing a pressure test with nitrogen, while good and I would also recommend it.. is NOT a solution to an evacuation. People doing this DIY are buying cheap fittings often. What holds positive pressure, does not hold a vacuum. PTFE seals for example are great at holding positive pressure.. not very good at holding a vacuum.

If you are pulling a vacuum through a 1/4" hose and a cheap vacuum pump it can take way longer than 2 hours. You cannot just blindly guess how long you think it will take. If you have one fitting that has a bad o ring.. yes JUST ONE.. your vacuum may pull to 50,000 microns but no lower... you would be leaving moisture in the system. But your cheap manifold gauge may still read -30hg

Gauges that read "-30hg" are not designed for negative pressure.. all they are telling you is that you are lower than normal atmospheric pressure. If you want to personally do this on your own system, then whatever.. but one thing I will not stand for is letting people who know no better be lied to and destroy their new system because some idiot told them it was OK to set up a system without a proper evacuation. While -30hg may translate in math to 0 micron.. they dont read that. If any of your morons ever tested this yourself you would know that.


r/DIYHeatPumps • • 11d ago

I think I picked the worst possible spot for my mini split

3 Upvotes

I'm planning to install a Costway mini split in my living room, but I'm having second thoughts about where to mount the indoor unit. The spot I picked is above the couch, about 7 feet off the floor. It's an exterior wall, so the installation would be pretty straightforward. The problem is that the couch sits directly below it, and my desk is about 15 feet away on the opposite side of the room. I'm worried the warm air will mostly circulate around the couch while the desk area stays cold. There's also a tall bookshelf near the couch that might interfere with airflow.

I could move the unit to the wall facing the couch, but that would mean a longer refrigerant line and more installation work. I've been reading mini split installation tips, but most focus on mounting height and clearance rather than how furniture affects heating. Would you keep it on the exterior wall or move it for better airflow? I'm trying to figure this out before the installer starts drilling.


r/DIYHeatPumps • • 12d ago

Mini split compressor acting up after only 2 weeks?

6 Upvotes

Got a 12k BTU Cozeware mini split installed about 2 weeks ago, and it was working just fine until yesterday. Now the outdoor unit is making a weird sputtering sound, keeps struggling to run, and shuts off after a few minutes. Anyone else run into this with a fairly new unit? Wondering if it’s something simple like low refrigerant or a leak, a bad control board, or if I just got a dud compressor. Pretty frustrating for a unit that’s barely 2 weeks old.


r/DIYHeatPumps • • 12d ago

Mrcool on oil furnace

2 Upvotes

I have a AC coil on top of a oil furnace that I want to swap out with a 5 ton heatpump coil from Mrcool. The current plenum is about 4 inches. Anyone has experience of installing a Mrcool coil in this setup. My main concern is the drain pan will melt from the high heat of the oil furnace


r/DIYHeatPumps • • 13d ago

MRCOOL Mrcool install

Post image
30 Upvotes

How did i do? 18k Easy Pro Mrcool 5th generation, I'm 79, I've done a little bit of everything but this was a great project for me. Took me 3 days for the install and a few more days triple checking for leaks. We installed baseboard electric when the wife and I built our house (1973) electric rates were great back then. When our central air continued to give problems I decided this was a great option. Only been down in the 30s so far and it's doing great,1300 sq. Ft. House and we keep 2 of the 3 bedrooms closed.