r/ElectricalHelp • • 6d ago

Voltage Regulator?

Having land issues hooking up my mother's trailer home and been waiting 10 yrs for a power line extension so I ran a 12 awg extension cable from my house (300 ft) to run her breaker panel. But the voltage drops down to about 90 volts when loads like the refrigerator kicks, which limits what she can turn on until the fridge kicks off. So I'm looking install a digital voltage regulator for her (like the Larson Electric 10kva single phase VR about $7K). Was wondering what the expert opinions are on this. I know that upsizing the cable to #2 or so might be acceptable but I'm not sure if this will bring the voltage drop up to an acceptable level. TIA all.

3 Upvotes

28 comments sorted by

5

u/davethompson413 6d ago

You might spend less than than that just running the right wire and circuits to the site.

0

u/These_Score_1250 6d ago

Good point. I'll have to do a load calc and price out the wire.

2

u/Connect-Preference 6d ago

RV people see this problem frequently. One common solution they use is to install an "Autoformer" at the point of use. This autotransformer can step up (or down) the voltage as needed, even switching as the load changes. Approved for use with RVs, not something you would use in residential.

One common brand is "Hughes Autoformer." It's a good idea to use a heavier wire gauge (lower number), too, but won't have to be as heavy as it would with no autotransformer.

1

u/These_Score_1250 6d ago

Thanks much, I will definitely look into this option.

1

u/Puzzled-Act1683 6d ago

It's an option, but it trades current for voltage, so the load on the wire increases, and you'll need to keep that in mind. 15 amps at 120 volts becomes 18 amps at 100 volts, etc.

Larger wire is the correct solution. Try a voltage drop calculator.

https://www.calculator.net/voltage-drop-calculator.html

For that one, set the conduit type to PVC and the power factor to 1.0 for the safest results.

8

u/upkeepdavid 6d ago

300 ft on 12 awg is too long a distance. Beef up the wire.

0

u/TnBluesman 6d ago

Didn't OP mention he's a vegetarian?

3

u/Ok_Bid_3899 6d ago

Do it correctly install a larger circuit with proper wire size to accommodate the voltage drop.

3

u/OldGirthyGuy 6d ago

Bigger wire period.

Here is #12, @ 100meters/300ft, with a 30amp load at the end of rhe wire

2

u/OldGirthyGuy 6d ago

Here is the same 30A load on the end of #2 wire.

2

u/OldGirthyGuy 6d ago edited 6d ago

Here is a 50A load on the end of #2 wire. You are still at around 115v, which is acceptable.

Voltage drop calculator from Electrodoc App.

1

u/Tesla_freed_slaves 6d ago edited 6d ago

600” of #12 Cu is about 0.95 ohms, so it looks like your mom’s icebox is pulling a 30A starting surge. #2 Cu would reduce the voltage-drop by a factor of 10.

Consider buying your mom an inverter-drive type refrigerator, which runs continuously without shutting off. Can you move her trailer any closer to your home service-panel?

2

u/These_Score_1250 6d ago

Not an easy option, her water and sewage are already and would have to be moved as well.

0

u/Tesla_freed_slaves 6d ago edited 6d ago

Figure on a 300’ trench, 24” deep, 300’ of schedule-80 PVC, 3 pull-through condulets, and 1200’ of Cu for starts. No underground splices. Would your mom be happy with an Amish propane refrigerator?

1

u/qvalff8 6d ago

Consider the battery, inverter and maybe even solar option. 5-16kWh 48v lfp battery, 8-12kW inverter, some amount of solar (optional). You charge the battery at 300-500W (might be better to convert your extension cord to 240v to minimize voltage drop). None of this code, but you're obviously fine with that based on running your extension cord 300ft.

Basically the battery acts as a buffer for your mom's electrical loads.

Go on YouTube and watch will prouse on his hand cart builds. Something like that will be a few grand (3-8k depending on battery size and power).

1

u/RespectSquare8279 6d ago

Most 120 volt appliances will also run on 110 volts but they won't be happy. There are probably cheaper than $7,000 solutions to your mom's trouble. I would explore #6 or #8 welder's extension cables ; you just have to find some that are OK in the outdoors for UV. The voltage drop with 300 feet of #6 will be just under 3% which would take your nominal 120 volts down to 116 volts. Is this code? NO! ; will it work, yes.

It was suggested previously that you get your mom an inverter type fridge. This is a good idea as they have far fewer duty cycles where the compressor turns on and off causing those demand surges The compressor in the inverter fridges slows down and speeds up and that does not cause the notable surges.

1

u/kona420 6d ago

4-4-4-6 or 2-2-2-4 aluminum, youre gonna be in for about a grand in materials and a few days digging but it'll be fully solved. Wire as a multi-wire branch circuit with a dual handle breaker, two circuits share a neutral. Little bit more wire cost for double the power.

Dont bother with smaller gauges or copper you are paying just as much or more.

Nice thing with a MWBC setup is the neutral currents cancel each other out. So loading up both circuits at the same time actually increases voltage. So you'd plan to have some continuous loads like lighting on the opposite circuit from the fridge.

Phase two, add a subpanel, that triggers a requirement for two ground rods but thatll be a bit safer.

1

u/Sacrilegious_Prick 5d ago

Find a couple surplus. transformers. Step up to 600 at supply and back down at the other end.

1

u/ozone_one 5d ago

As everyone else has stated, the correct solution is thicker wire.

An alternate idea, depending on your average weather conditions, might be to ground-install a few rigid full-size solar panels and hook them up to a small lithium battery bank via a small inverter/charger. Given the current cost of copper, it might even be cheaper than running new wire, since solar panels have gotten so cheap. The inverter and battery would handle any large or startup loads locally, the panels could recharge the battery during the day, and you might even still be able to draw a small amount of AC through the line you ran to give a bit of charge as well.

What does the AC voltage read when the fridge is not on? Just curious, I wouldn't think that a small RV-size fridge would draw that large amount of current on startup; wondering if maybe the compressor motor is starting to fail.

Also, if this hasn't already been done, replace all of the lighting in her trailer with LED-based lights. The amount of energy savings to be gained there is pretty amazing compared to old school bulbs.

1

u/Ok-Sir6601 4d ago

That's an undersized wire

0

u/FreddyFerdiland 6d ago

the voltage lose is power being lost as heat in the cable... heating power = voltage drop x current

0

u/EdC1101 6d ago

Wire gauge for electricity is sorta like pipe size with water.

A small pipe / tube for a refrigerator ice-maker can provide full pressure, but cannot move the volume of a garden hose.

When the length is extended, friction against the interior wall further reduces flow.

Restrictions upstream, (transformers & distribution equipment,) can further limit power available.

That said, increasing wire size to the trailer will help, but it might simply move the problem upstream to the house.

Distribution to the house will need to be improved also.

0

u/silasmoeckel 6d ago

7k Is a bit crazy.

Get a hybrid inverter that can deal with a genset and other unstable inputs. Victron is big in this space. Add a battery should be ~1500-2k bucks for a 5kva setup. You can now run the camper off a lamp cord if you want as it's just the average going through it. She will see a rock steady 120v and be able to use more appliances at the same time (the difference is taken from the battery).

Considering #2 copper prices the inverter/battery is the cheaper option.

2

u/Major_Tom_01010 5d ago

Buddy could run #2 aluminum on pylons for around $1k

1

u/silasmoeckel 5d ago

#2 Duplex AL is still ~500 and 300f is a lot of supports to put in (and ugly).

-2

u/TnBluesman 6d ago

A voltage regulator ain't gonna help ya much, sport. You're gonna have to run a MUCH bigger wire. The kind that don't come with plugs on the ends. Hell, even going up to a 10ga extension would be a big improvement. But I'd recommend #8. UF cable would be good. That's Underground Feeder cable. Rated for direct burial. (We used to call it Mother- In- Law wire because it was rated for direct burial. )