r/ElectricalHelp • • 5d ago

GFCI - High Temperature

I pointed my thermal gun at the GFCI in the washroom. It read about 36+ degrees Celsius(96 Fahrenheit). This seems high, there is nothing plugged in.

We replaced it with a new outlet, same thing, it runs hot.

The outlet feeds the washroom and then carries on to another outlet on another floor.

Is this normal? What’s the issue? The other outlets in my house are room temperature.

Looks like it one of the gfi loads feeds two spare bedrooms ceiling fans/lights, and the other feeds an outlet in the other washroom on the main floor….this is weird, right?

0 Upvotes

15 comments sorted by

4

u/trekkerscout Mod, Master Electician 5d ago

GFCI receptacles contain electronic circuits. Being a little warm is not unusual.

1

u/Unique_Acadia_2099 5d ago

Bingo. There is a printed circuit board inside with a power supply that is on all the time. Power supplies are never 100% efficient, so there is heat produced. Not a lot, but it is trapped in that box with the outlet.

1

u/jayv1980 5d ago

Just to see what else may be protected (and being powered through) that GFCI, hit the test button and see what shuts off. You might have bathroom(s) lights and receptacles running through that gfci... and honestly who knows what someone else may have connected to the load side of that GFCI...maybe without even knowing it.

1

u/Tatortotter123321 5d ago

Looks like it one of the gfi loads feeds two spare bedrooms ceiling fans/lights, and the other feeds an outlet in the other washroom on the main floor….this is weird, right?

1

u/jayv1980 5d ago

Gotcha. That could explain the heat. Its definitely not how youd install the bathroom gfci circuit to current code... and I think youd probably have to go back quite a ways to find a version of the nec that would have allowed this. though its not necessarily an issue. Its made some things safer if not susceptible to nuisance tripping...which you havent mentioned experiencing.

If you want it done to current standards thatd be beyond the scope of reddit since it covers quite a few areas of your house. But if its not giving you any trouble Id leave it. 90 F isnt dangerous, but its probably shortening that gfcis lifespan by a bit.

1

u/TnBluesman 5d ago

I've been on this rock 75yrs and I really don't think the NEC, NFPA, NSF or CIA ever allowed THAT kinda chain mail from a single GFCI.

1

u/KeanEngr 5d ago

When you say it’s “warm” is the heat coming directly from the plug or are the wires connected to the load side of the plug warm? As mentioned by u/garyku245 there might a ‘leaking air duct’ in your wall blowing hot air into that outlet. With the outlet installed and a cover plate on, do you feel warm air blowing out of the outlet itself?

1

u/Tatortotter123321 4d ago

No warm air. I have a thermal monitor and when I point it at that outlet it’s 36+ degrees in the middle. Any other outlets in the house there are no thermal signatures (room temperature). I also pointed it at my breaker panel. The breaker with a test button on it (bedroom) is showing 37 degrees, all other breakers show no heat signatures?

3

u/Cloudy_Automation 5d ago

It may also feed the lights and fan in the bathroom. If the wires are properly torqued, it shouldn't get too warm. Still, wire is usually rated for at least 60C.

If you have an amp-clamp meter, you can try to figure out where the current is flowing. Something is using power.

1

u/N9bitmap 5d ago

Pass through load, normal heating below 40C. Maybe worry above 50C.

1

u/garyku245 5d ago

If that outlet is feeding power to other outlets, it may be heating due to a load on the other outlets. It also might be above a heating duct in the wall or a register.

1

u/TnBluesman 5d ago

Good answer.

1

u/JasperJ 1d ago

How much are the load wires drawing, and how hot does it get without them connected?

A GFCI is gonna have some losses, it typically is specified at a watt or two for the ones I know.

0

u/Comfortable_Host1697 5d ago

There may be a loose connection somewhere else or there.

0

u/Comfortable_Host1697 5d ago

Bad splice, incorrect splice, maybe a voltage leak to ground. You need a tester and qualified electrician. This should not be this hot. Id recommend turning it off.