Multiple 14-30R receptacles?

Right now I want to install an outside 14-30 inlet receptacle and a panel interlock for my generator.

In the future, I am going to want the receptacle inside near the panel, because I hope to install a battery backup capability. I can envision a use case where direct generator power might still be a contingency.

Can I install one 14-50 inlet outside and one inside now, and wire them together? I would only ever use one or the other.

3 Upvotes

14 comments sorted by

6

u/wowfaroutman 1d ago

Regardless of whether you're considering an interlock with 14-30R or 14-50R inlets (50 amp recommended for future proofing), you shouldn't do what you're proposing without a double throw switch to switch between the two inlets. Otherwise if one of the inlets is being used, the unused inlet male connector will have live pins.

2

u/SwornBiter 1d ago

I got you. In my particular case, having no kids or dogs, a 6-foot fence, and the issue only being present when the grid is down and I’m using reserve power, the risk is very small. I will go with the one outlet I need, though, and reconfigure when the battery solution comes along.

1

u/Sharonsboytoy 1d ago

This is a good decision. Just one outlet, as you don't know what the future might bring.

1

u/Puzzled-Act1683 1d ago

The only acceptable risk level here is zero. Don't wire two inlets together without an A/B switch between them.

That isn't what you really need, anyway.

You need an inlet outside, wired directly an outlet inside, and connected to nothing else. Then the "real" inlet inside, that feeds into your panel, is connected only to the panel, and to none of the other stuff. Then a short male to female jumper cord inside, to connect outlet to the inlet for powering the house directly from the generator.

When you add a power station, you remove that indoor cable from the outlet, and plug it into the power station, to power the house... and plug the power station into the outlet, to charge it from the generator.

My indoor setup. The outlet is fed from the outdoor generator inlet, and the inlet feeds to the panel. No internal connection between them except the grounding wire, which grounds the generator frame through the outdoor cord regardless of what is connected inside.

1

u/biblicalrain 1d ago

This is an interesting solution. Why this over a three pole switch?

1

u/Puzzled-Act1683 1d ago

Thanks. An isolation switch would allow you to power the house from either of two inlets, but it doesn't solve the problem of charging a power station from the generator, while simultaneously using the power station to power the house.

If you only had an outdoor inlet, an indoor inlet, and a switch, you'd need an extension cord from outside to inside to get generator power to the power station.

That's kind of what my setup boils down to – the isolated outdoor inlet to indoor outlet circuit behaves like an extension cord through the wall, so it supports either directly powering the house from the generator, or putting a power station inside while feeding it from the generator outside.

To charge the power station from the grid, while no outage was occurring, you'd plug it in somewhere else.

1

u/biblicalrain 22h ago

Could you not have one inlet that's outside, and then once the panel is powered, just plug the power station into a wall outlet? I guess one downside is that this would limit the charging to 120V at 15A.

Just asking to understand how this works, this is something I'm looking to set up.

1

u/Puzzled-Act1683 17h ago

The power station is powering your house, so any wall outlet power would be coming from the power station. If you plugged it into a wall outlet, it would be trying to charge itself. The idea is to charge it from the generator while it's powering the house. When the load is higher than the generator, this slows the power station's discharge rate, and when the load is lower than the generator, all the surplus goes into the battery, allowing you to cut off the generator for hours at a time.

My setup gives you both options:

Generator -> house

Generator -> power station -> house

To do this with only a conventional inlet outdoors, you need two large extension cords under the garage door or through a window from outside to inside and inside to outside, one to feed the generator into the power station and the other to feed the power station into the outdoor inlet. That's exactly what I did before I rewired it the way it is now.

My power station is 7200 W continuous/14400 W peak, but I can charge it with my smallest generator, only 2600 W, while it is delivering more power than that into the house. I usually use a larger generator to make the charging faster, though, and the solar panels feeding into the power station reduce the amount of generator runtime even further, and of course I try to keep my loads minimum. I can get by with 8 hours of the generator running per day while having power to everything in the house all day and all night.

0

u/nunuvyer 1d ago

You need a double pole, double throw switch, not a 3 pole. Normally you just common all the neutrals with each other and likewise the grounds so that you only need to switch the hots.

1

u/nunuvyer 1d ago

Even if it is just you, you can't create a situation where you have live prongs sticking out of your generator inlet. However, it would be easy enough to set up a manual transfer switch to switch between the two.

https://www.amazon.com/Transfer-Generator-240-Volt-General-Duty-Double-Throw/dp/B0DLGGRNLT

One inlet would feed into the top contacts and one inlet would feed the bottom contacts and the middle contacts would go off to your panel. Only one of the inlets could be live at the same time, depending on which way you throw the handle.

1

u/GreatPlainsFarmer 1d ago

"can't" and "shouldn't" are not the same thing!!! šŸ˜‚

2

u/Dramajr316 1d ago

I was going to make this exact point. A selector switch between these would essentially 'cut' the unused inlet, so no fear of unintentional backfeeding to something you weren't intending.

1

u/orlinsky 1d ago

You cannot wire them together if for no other reason than when you open inlet 2 while inlet 1 is powered, you are exposing bare metal contacts to the world that are hot.

1

u/goldcoast2011985 1d ago

Since the battery will be taking in power from the panel sometimes and putting power into the panel other times, would hardwired to a battery controller make more sense?