Insulation help.

I’ll try to keep this brief. I recently got a multi position ladder for another project. After I finished I decided to go up and checkout my attic. The reason being, I have this spot on my ceiling that looks like water damage. Upon making my way above my bedroom. I noticed there was no insulation above the room and the vapor barrier has moisture trapped underneath it. Anyone who has ideas of how to fix this I would appreciate it!!

2 Upvotes

7 comments sorted by

4

u/IamTetra 1d ago

It's your lack of insulation in that area, don't know why the void is there, but without the insulation, that drywall is getting colder than the humidity dew point in your attic which is condensing moisture. If the void needs to remain, remove the moisture barrier to allow evaporation.

1

u/J-J-J22 1d ago

I have two areas in the home where the ceiling goes up higher than the rest of the ceilings. This is above one of them. So remove the moisture barrier and allow it to dry out then place a new barrier and insulate?

1

u/2Confuzed 2h ago

Don't remove the vapor barrier, it will dry out fine once you restore the insulation.

Essentially, you want that plastic to be at the room temperature so it doesn't provide a condensing surface. To get there, you need insulation. Once its properly warmed, the water that is there will evaporate and become part of the room's humidity. It might take a couple of days, but it will dry out.

Really strange that that entire section was left uninsulated,

1

u/IamTetra 1d ago

But you certainly have a distinctional moisture control system in that particular area. intuitively, the lack of condensation everywhere else that has insulation points to that being the problem, so i'd match what the rest of the ceiling is doing..like vapor barrier and type and thickness of insulation.

3

u/Novus20 1d ago

How old is the house?

4

u/J-J-J22 1d ago

It was built in 2023.

1

u/Hyperreal8957 1d ago

agree with the dew point take. wet spot under the vapor barrier usually means warm house air is reaching a cold surface where the insulation is missing. i'd pull back the barrier, let it dry fully, then add insulation to match the rest of the ceiling before closing it back up. also worth checking for air leaks around that vaulted section and any bath fan ducting, and if the drywall got soaked have a pro take a look.