Kitchen suppression temperature code

7 Upvotes

6 comments sorted by

2

u/EC_TWD Oct 22 '26

This is a great thing, but companies are gonna need to begin stocking extra recharge chemical and rebuild components!

When I was a full time tech I’d split a bag of 500 links with another tech in January and end up throwing a few away in December. I’d go through 10 bags of 360 a week and maybe 1 bag of 450.

4

u/Many-Move8141 Oct 22 '26

Links do not have an expiration date until they are installed. In which case, it's 6 months after installation.

  • You are supposed to document what year links were installed?

2

u/EC_TWD Oct 22 '26 edited Oct 22 '26

True, but my company was incredibly strict with link control and chain of custody because they’d been sued once upon a time. Every fusible link that we removed was put into a manilla envelope, dated, job #, signed off by customer and tech, and then put into a banker box in our warehouse that was retained for 2 years and then tossed. They audited the link pouches to tech work orders every month and would pull 2 bags per tech, per week and look at them to ensure they matched reports for quantity, temp ratings, and dates.

Once a calendar year rolled over any links dated the prior year were tossed. The overall total was pretty low because they kept a tight control over them and the leading year links would start showing up in Oct/Nov. They tried to keep current year links stocked through the first week of December and would hand out leading year dated as we ran out. We went through a lot.

Having worked for a company that had been through that was a great thing because I learned how to be risk-averse and proactive. Customers notice and it stands out from fly-by-night outfits and you no longer compete with price, something that my competitors still haven’t figured out because they still try to beat me by being the cheapest.

1

u/firesafecivilian Oct 22 '26

You know I would like to consider this , I by my means use a temperature gun and or go with the rating the Accept design had if it’s a newer system . Now with that being said I do technicians that don’t do what I do , they say 450f all around or may only use 450f ml if a fryer is involved and use 360f the rest of the appliance lineup

1

u/imalrightspider2k Oct 22 '26

Careful with temperature gun. Those can measure reflected heat. Probe sensor is going to give a more accurate temperature reading of the air above each appliance

1

u/haydenkayne Oct 24 '26

When in doubt, 450 it out.