Does this make sense?

Post image

I saw a build not long ago for a similar project that led me into this purchase, but I can't locate that now. 🤦‍♂️I bought a hand truck, 2 48v 100AH batteries, and a 5000 watt pure sine wave inverter. I'm trying to have a mobile UPS that I will have connected to my networking and server equipment most of the time, but I also have an off grid cabin that is currently running off of a bank of 12v lead acid deep cycle batteries and one 200w solar panel with a 2000w inverter. This has worked for 7 years now, but those lead acid batteries are starting to lose their top end. Also, it gets quite warm in there over the summers and requires me to run a generator to power an air conditioner and mini fridge simultaneously. I would like to avoid that and take this hand truck with me when I stay there for long periods of time.

I have some 2 gauge cables for the battery connections between the two batteries and connecting to the inverter. I have some 12 gauge romex for connecting the outlets. I have some 6 gauge thhn for the connections between the inverter to the load centers. I was going to put one 50A single pole, before the two 20A breakers in a second load center. Does that all make sense?

The only thing I haven't purchased yet is the load center and breaker for the 50A connection. Also, I believe there is a breaker already inside the inverter between the batteries and the inverter, but I could be wrong about that. Do I really need inline fuses between the batteries and the inverter if so? Also, I know this probably isn't the best, but I was just going to cut the female end off of a 12 gauge outdoor extension cord for the AC in connection to the inverter.

2 Upvotes

3 comments sorted by

4

u/Puzzleheaded_Pen3164 6d ago

I'd keep those two 48V batteries in parallel so you stay at 48V for the inverter, and still put a fuse or breaker on the positive close to the batteries even if the inverter has one inside. A short in the cable won't wait for that internal breaker. I'd also skip cutting the end off an extension cord for the AC input and use a proper inlet instead, so you don't end up with live pins sitting exposed.

1

u/OrphanSolarHelp 5d ago

One mismatch to sort out first: the 200 W panel and whatever charge controller runs the 12 V lead-acid bank won't charge the new 48 V batteries. You'll need a charge controller rated for a 48 V bank, and 200 W of panel is unlikely to keep up with an AC plus a mini fridge anyway. Before buying panels, add up the daily watt-hours. For the fridge, its label kWh per year ÷ 365. For the AC, running watts × hours. Size the array from that number. And keep the old 12 V system separate from the new pack, since they're different voltages and chemistries.

0

u/TheRealSimpleton 6d ago

I am looking into moving up “north” New York State, Maine, Michigan or thereabouts. I’m interested in maximum freedom and land, but I am worried about the tax burden. I can work virtually so I’m not worried about finding work but I would like to have forest land to work and develop and to maintain and enjoy. Also I want to stay cool. I live in South Florida and am tired of the heat and COL. I love some of these places I’ve seen for sale, some with outhouses, etc. I just don’t have any experience living like that especially in the snow and would welcome any guidance.