r/PLC • u/Disastrous_Depth_176 • 2d ago
PLC Question Monitor a multiple instance DB
Hi all
I hope you are well
how I can monitor this Fb .it is a local Fb as the photo shows and there are several of them in this fb205 .
any idea please
18
Upvotes
5
u/The_Infinite_Carrot 2d ago
Open the calling block.
Go to Debug > Operation and select Test Operation.
Go online with the block.
Right-click the multi-instance FB call you want to inspect, then choose Called Block > Monitor with Call-Up Path.
2
u/KahlanRahl Siemens Distributor AE 2d ago
Looks like that’s in the statics of the block interface. Monitor that from the instance DB of the calling FB.
7
u/danielv123 2d ago
You need to change the call environment for your monitoring session: https://support.industry.siemens.com/cs/document/21671563/how-do-you-monitor-a-block-with-the-desired-call-environment-in-step-7-?dti=0
1
u/Mother_Mail_8831 1d ago
open the instance db of the calling fb (1_A03_JIG_BJ1 in your screenshot), turn monitor on, and expand the statics down to the instance you want (AO3VTC in that network). same path works in a vat: "1_A03_JIG_BJ1".AO3VTC.YourVar. if the call-up path still comes up empty, the call environment has to be that parent db, network 92 actually has to be running (those contacts on the EN), cpu in test operation, and the online block not showing as different.