Structural Analysis/Design What are those things doing?

Post image

Those are sprinkled in my building in certain pathways. They're all bolted to the ceiling only, usually where the sidewalls are made of cinderblocks. Curious what they're doing and why only attached to the top.

258 Upvotes

101 comments sorted by

196

u/foxfrank123 2d ago • Bravo

Out of Plane support for the Masonry Wall at the top. The caulk joint at the top allows the floor to deflect down. The steel angles are slipping up and down along the wall when the floor deflects. You will have the exact same connection on the other side of the wall so that the top of masonry wall is supported out of plane in both direction. You need that because the wall is considered pinned at the bottom and pinned at the top and spanning vertically from bottom to top.

4

u/dunderthebarbarian 2d ago

Is the masonry wall freestanding or load bearing then?

-16

u/Duncaroos Structural P.Eng (ON, Canada) 2d ago

gut feel this would be load bearing; if it was non-load bearing, then it would be excessive to have that many angles.

10

u/Responsible-Sea-4685 1d ago

Wrong. The reason it has the angles is because it is not load bearing

-1

u/Duncaroos Structural P.Eng (ON, Canada) 1d ago

You know, once I read your response I finally understood I was going down a rabbit hole with tunnel vision. Thanks mate for the most simplest correction!

12

u/Beneficial_Net8417 2d ago

Definitely not a load bearing. Looks like a PT deck. The cmu walls are added later. There will typically be rebar tied into the deck sticking out of the floor. The cmu wall is built on that. B ut there is nothing tying the wall into the ceiling. That’s what the brackets are for. I’m just an electrician but the brackets are probably required for seismic also. So the wall doesn’t fall over in an earthquake.

Where I’m at they put in steel plates in the pt deck and weld those brackets in.

-2

u/Duncaroos Structural P.Eng (ON, Canada) 2d ago

Retrofits are a thing. You don't have x-ray vison for a picture to see any rebar from the hollow cores of those CMUs to the slab. You can see from the side of the pic there's more of these angles on a different wall with similar spacing.

Regarding seismic, lateral forces out-of-plane to that wall would be going through that slab to stiffer locations. Compressive buckling would be more what I would consider to be the reason for these angles, so the top of the wall is considered 'pinned' instead of a free end. A non-load bearing wall has much less compressive load than load bearing by definition, which is why my gut feel is that it is load bearing.

Now, without drawings no one can answer with 100% certainty, so I'm not saying I'm right either, but I did say "gut feel", not "definitely".

2

u/ResearcherFit6960 1d ago

Lmao yeah , the inch of caulking of on top is doing a lot of heavy lifting,

-11

u/No-Violinist260 P.E. 2d ago edited 2d ago

You don't have to have this connection on both sides, this connection can be designed for pressure and suction on one side

Edit: I see the down votes and as installed this detail can't take pressure and suction, yall are correct. I use this detail with the slotted hole like OP stated. Dovetails or rebar detailing to not take gravity can also have the same effect

46

u/lieutenantnewt P.E. 2d ago

That would require a vertical slipped bolt into the masonry wall through the vertical leg of the angle though. Since we don’t see that in this picture, I’d say it’s safe to assume there are angles on the other side as well.

2

u/Ko0ntz P.E. 2d ago

L6x4x1/4 LLV BTB was called our on plan without an abbreviation table.

Interpreted as Bluetooth bolts. /Satire

-7

u/Osiris_Raphious 2d ago

Otherwise the design software model spins about its axis and results don't converge.

10

u/NorthEndD 2d ago

They fixed that in GTA6.

0

u/[deleted] 2d ago

[deleted] — view deleted comment

29

u/Disappointed_Horse 2d ago

The angles are providing lateral restraint to the top of the wall. Infill walls need to be designed for a nominal lateral robustness load. The gap and compressible filler at the top ensure no vertical loads are transferred into the wall, meaning that the wall is non loadbearing.

0

u/[deleted] 2d ago

[deleted] — view deleted comment

5

u/runawayasfastasucan 2d ago

No its not how you understand it, you just thought it was load bearing.

5

u/Tasty-Strawberry-155 2d ago

You are frightening

4

u/RU33ERBULLETS 2d ago

What did the comment say? boo?

1

u/coroyo70 Architect 2d ago

Prob something silly like “it's load bearing”

15

u/largehearted 2d ago edited 2d ago

This is the common detailing choice for top restraint of nonloadbearing walls in both of the major American cities I've worked in, and I've seen a lot of cracked CMU partition walls from past decades that I think would've been fine if they had this kind of detailing

I've also seen it constructed with no joint filler at the top and just an airgap between the structure above and top of wall

6

u/kickinthisshit 2d ago

Yeah we use this detail alot in the UK too, this bracket seems a bit overkill though in terms of size and bolt diameter.

0

u/[deleted] 2d ago

[deleted] — view deleted comment

11

u/tiltitup 2d ago

Are you using ai to answer comments

0

u/[deleted] 2d ago

[deleted] — view deleted comment

5

u/runawayasfastasucan 2d ago

You need to adjust your attitude. In one comment you say it must be a load bearing wall, in the next you pretend like you assumed it was not.

4

u/AlbatrossRich8724 PhD 2d ago

No. This is considered non loadbearing, other wise there really wouldn’t be much purpose to those angles. You’re using them to hold the wall where it is in the direction orthogonal to the plane of the wall.

112

u/Superb_Sea7721 2d ago

Not an engineer. I'm a misc steel estimator in Chicago, and these show up on almost every job with CMU partitions. On the drawings they're usually a typical "top of wall bracing" or "head restraint" detail: clip angles on each side of the wall, at whatever spacing the engineer calls out, fastened to the deck or joists above. They're not meant to carry any load down into the block. That's why there's a gap at the top with the caulk joint. The floor or roof above can move up and down, and the angles just keep the top of the wall from moving in or out. From the bidding side, they're easy to miss in a takeoff. It's one small detail on one sheet, but on a school or a big warehouse with lots of block walls stopping at the deck, it can add up to hundreds of pieces.

25

u/SCL__ 2d ago

I can see how they could be missed. “Miscellaneous metal”.
My friend was an estimator and would go through huge sets of drawings and color code the different materials with markers.

5

u/Hot_Departure9115 2d ago

Yeah easy to miss because they're not shown on plan view or elevation sheets usually. They're only shown on detail sheets or listed in the general structural notes and you have to figure out how many you'll need.

7

u/Powerful-Interest308 2d ago

I had a cost estimator refer to them as 'Mysterious Metals'

2

u/bentrw 1d ago

Stealing this. Describes half my day on new plan sets

1

u/fuckschickens 2d ago

Or embeds not inplace when pouring a PT deck.

8

u/Ok_Leek_9664 2d ago

Also in Chicago on the GC side. Our estimators screw this up all the time because the masons want to F&I these now. The IMI is advocating for that (at least here they are) and our young estimators assume they got them.

3

u/Building-UES 2d ago

I point these out in the scope because I want the mason to supply them. H&B makes a product that conceals the clip. It makes the back of house spaces look neater. In finished spaces the drywall is tighter to the CMU.

3

u/82FALLOUT82 2d ago

This is exactly what they are, I will be installing a few next month on my project.

1

u/Junior_Example_923 1d ago

I love this. I'm in drawings all day long for my quoting and installation and I see all of the other trades and scenarios just freely available in front of me and I don't appreciate how the general public almost never sees the drawings, spec sheets, not the laundry list of RFIs and responses that shift throughout construction of a building

1

u/Medium-Sheeple-7085 10h ago

The word RFI practically sends me into a catatonic state.

20

u/wardenka 2d ago

It holds the wall horizontally

12

u/Human-Flower2273 2d ago

Restrain horizontal (out of plane) movement of wall

10

u/faileagle 2d ago

Head restraint for the wall

7

u/ThorsMightyBackhand 2d ago

Those angles brace the top of the CMU wall so it doesn't push out one way or the other. The slab above does not bear on the wall and won't hold it in place.

6

u/_Rob1 2d ago

Head restraints

11

u/Frogalone 2d ago

Generally you don't want a non-loadbearing wall to become accidentally loaded. You do, however, want the wall to remaining upright and plumb. A series of angles both sides of the wall with sufficiently long legs and fastened as shown will accomplish both objectives.

10

u/idledopamine 2d ago

I am an ironworker by trade for over a decade, these are seismic clips. They are intended to prevent lateral movement of the wall during any shift, as the wall is already strong in vertical compression.

8

u/GotNoPonys 2d ago

as an engineer I often get tripped up over words. "prevent" is too strong in this application. Unthinking people read that as "stop" movement. I would phrase it as "limit" movement during minor seismic events. We are in seismic zone 4, a red area on seismic maps.

4

u/reasonablemanyyc 2d ago

keep the wall from flopping over. Horizontal stability at the top as they are not pinned into the concrete. Walls were put up after the slab. Hope that helps!

6

u/Doagbeidl 2d ago

They do their best

-1

u/Marus1 2d ago

So they are me?

3

u/Brokenspade1 2d ago

Screams in: brick layer

Those are anchors for unattached walls. Basically it's too keep the free floating wall from tipping over in an earthquake. They also suck.

3

u/Impossible-Storage80 1d ago

Seismic clips to prevent lateral movement and provide lateral restraint incase of a seismic event

2

u/Fresh_Painting_5483 2d ago

Mostly I’ve seen this methodology as - for post installed NLB walls (after slab poured) & serves as a top fixing connection. The top of the wall should have some sort of compressible material that isn’t ment to take load

4

u/ramirezdoeverything 2d ago

Lateral resistant to the top of the blockwork wall. Usually this is provided by steel ties fixed to the underside of the concrete slab which are then built into the mortar joints of the wall, however this looks like a retrofit solution possibly because the ties were neglected to be installed in the first instance.

1

u/Key-Metal-7297 2d ago

I think they would be more effective in longer lengths of thinner material but I guess it works

1

u/SquirrelFluffy 2d ago

I see these in condos all the time when I do performance audits and it's (not) surprising at how many times I find them missing their bolts to the slab.

1

u/OptimalRip4766 2d ago

Building code requirement to resist minimum lateral loading on masonry walls. Life safety issue, even if considered non load bearing the intent is to keep the wall from falling over, 130pcf tipping over is dangerous especially if on an egress path during an event.

1

u/zapzaddy97 2d ago

On my last job the steel workers were installing these and maxing out their SDS bit into the slab. They ended up going into so many of our conduits in the slab. We had even found a few of these wall plates live as they only hit a hot and didn’t short out when they installed the sleeve anchor.

1

u/workmyiron 2d ago

Fuck cmu clips nothing like overhead hammer drilling at 5 am

1

u/InTheLurkingGlass P.E. 2d ago

To me this looks like lateral support for a non-load bearing wall or partition wall.

1

u/bigdogbill12 2d ago

Lateral support for seismic so the wall doesn’t fall over.

1

u/RelationshipHeavy386 2d ago

They are either on both sides or installed incorrectly. Probably the latter. Hilarious.

1

u/longlostwalker 2d ago

I suspect stopping the wall from falling over in the case of some unforeseen circumstance

1

u/Perry_Mortem 2d ago

Is that some type of compressible material along the top?

1

u/Worried-Flatworm2472 2d ago

They hold the top of the block wall in place preventing it from moving . If it’s both Sides it doesn’t need to be bolted to block

1

u/djbj1987 PE, SE 2d ago

Sort of obsurd spacing, 16”oc?!

1

u/raypell 2d ago

They print money for ironworkers, easiest work there is

1

u/h0zR 2d ago

Stopping the wall from transitioning to a rubble pile

1

u/ReplyInside782 2d ago

Used on non load bearing CMU walls to brace the top of the wall since the wall isn’t tied in to the slab above. This is purposely done so that your CMU walls don’t inadverantely contribute to the building lateral system

1

u/LevelDegree5627 2d ago

CMU clips to keep wall plumbing to not sag

1

u/OverallDimension7844 2d ago

Just hanging out

1

u/Original_Freedom3232 2d ago

Just hanging out

1

u/Frogalone 2d ago

You normally don't want a non-load bearing wall to become loaded accidentally. You do want the wall to remain upright and plumb. The angles, or similar, fastened through the horizontal leg to the slab in this case accomplishes both objectives.

1

u/No_Valuable_1738 2d ago

PTSD is what it is for me

1

u/rampant_bastard 2d ago

Most schools require them for non-bearing cmu partition walls for top of wall stabilization the LL does not attach to the cmu

1

u/Wonderful_Signal8238 2d ago

ruining my life is what they were doing my first year of apprenticeship in the bricklayers union. i put ~2,000 of them in one big building by myself. it took a year and a half and a pinched nerve.

1

u/Critical_Degree3450 2d ago

Minding they own business. Who are you to try an throw shade on them

1

u/wiwcha 1d ago

Stopping the wall from falling over.

1

u/Upset_Practice_5700 1d ago

Way to close together. Bad understanding on the specifiers part.

1

u/Mysterious_Basis8023 1d ago

The wall is being braced to slab. The wall was built after slab… see tooled joint at wall top

1

u/Plus_Importance_6582 1d ago

They keep the roof from floating away. Either that or they stabilize the wall.

1

u/Additional-Face2467 1d ago

wall head retainers

1

u/amazedbyitall 1d ago

These are restraint clips for walls not connected at the slab, columns or adjacent walls. Pretty typical spacing, 16” on center. They are usually staggered on the other side. The top of the CMU wall has 2 #5 rebar running the full length. This a very common detail in California.
Sometimes the gap at the top is filled with compressive material and covered with a waterproof elastic grout to prevent water getting into the building. On parking structures it almost always left open, except at the elevators.

1

u/millerscottp 23h ago

Non bearing wall lateral support. Those CMU blocks aren’t supporting the floor above so there isn’t anything holding the top. If you look closely, you can see the joint at the top is a different color. It’s a fire resistant caulking that allows the deck above to move up and down (deflect) as needed with only a negligible amount of force on the block wall. Similarly, the metal braces aren’t actually attached to the block, just the horizontal deck.

1

u/PlutoniumSpaghetti P.E. 21h ago

Looks like it braces the top of wall and provides a load path to the slab for any lateral loads on that wall to the diaphragm

1

u/Thatguyjavii 15h ago

... their job. Mind your own business.

1

u/tajwriggly P.Eng. 13h ago

You are getting a lot of different answers in here.

You will find these clips at the tops of non-loadbearing largely unreinforced masonry partition walls. There should be a gap with compressible fill materials between the top of the masonry and the structure above to allow the structure above to deflect and not impart load on the wall.

Masonry walls like this are typically assumed to resist out-of-plane loads with the wall spanning vertically - i.e. load being applied to the face of the wall gets transmitted to the floor and ceiling. You have to have pretty short lengths of wall to have it considered to span horizontally.

The clips create a pinned end condition at the top of the wall. Without the clips, the wall would essentially be cantilevering from the floor below. Pinning the top makes it a heck of a lot more stable, and capable of resisting out of plane loads such as difference in air pressure on one side of the wall to the other, impact loads, equipment supported from the wall, etc.

As a comparable example, consider stacking a bunch of books one on top of each other, and then pushing at them from the side. They will fall over pretty easily - but if you hold the top book in place, you will find it becomes a lot more stable.

The spacing of the clips typically is a function of the thickness of the wall and the spacing between returns (corners) or intersections with other walls. It can also depend on whether or not you have a bond beam in the top of the wall. A bond beam will lock a lot of the wall together and allow you to space the clips further apart.

We sometimes have contractors install these at a way tighter spacing than we ask for - and we're not about to tell them to reduce the number of them.

1

u/Pretend_Pea4636 11h ago

After an earthquake in Washington State we installed a lot of these. The intention was to keep the wall up during seismic activity instead of falling on occupants.

1

u/Few-Project-145 10h ago

Is there one on the opposite side of the blockwork wall?

1

u/Adventurous_Light_85 7h ago

They allow the deck above the wall to move up and down and support the masonry wall from moving left or right at the top

1

u/knackattacka 3h ago

They're preventing the vertical walls from shifting

1

u/AdAdministrative9362 2d ago

Might need to be fire rated too. I have used these for blast loads previously.

1

u/Anchor0355 2d ago edited 2d ago

Lateral restraint for the wall like others have said, but on a  wall panel that height and length it is unusual because the corners give it stiffness typically. If you do need additional restraint the usual detail is to include a windpost with wall ties to restrain the wall. Maybe the wall was built without considering the connection at the corners and it's not adequately tied in as they're not perpendicular, and it was discovered after the wall was built?

Edited to say, looking at the closest joint it's not toothed in at all and is acting as an independent panel. Most s.e.'s I work with would say this is not structural and therefore out of their scope so the brickies either should have tied it in or the site team asked the architect before building. Pretty sure this is an oh shit moment when someone saw what was built on site

1

u/SwimmerFriendly2900 2d ago

Keeps the pre-cast from shifting

1

u/charleyhstl 2d ago

I think they're supposed to be pointing at the red things

0

u/screwface_6 2d ago

It’s called a masonry head restraint. Usually these are hidden in the blockwork and protected from the fire. These look like an after thought and are generally considered rather ugly. They should also be made from stainless steel or galvanised to prolong the life. One of the bolts is very far out and hasn’t been drilled into the concrete far enough. My conclusion is, this was installed by cow boys on horses.

-1

u/cgnsatisfaction 2d ago

seismic clips

-1

u/Natural-Shirt-1463 2d ago

They probably forgot the dowels that connect to the slab, is this an exterior wall? They probably have a rebar at 16" OC too

0

u/droptopeclipse15 2d ago

I see lots of great answers here. Where I’m from we call them earthquakes clips. They’re not much fun to install. 

0

u/GamingSlob 2d ago

Their best. They're doing their best.

0

u/roooooooooob E.I.T. 2d ago

That’s classified

0

u/TomIsMinsky 2d ago

Enchated bistro