Structural Analysis/Design Noob question on load transfer due to construction practices in RCC Framed structures
Edit: This process is used in India.
Hello All, This is a question regarding framed RCC structures and construction methods. Particularly, the method of casting roof beams in framed structures.
The typical process is to raise the wall to the bottom of the roof beam height, and then cast the beam and roof monolithically, with the bottom of the beams resting on the wall below for the entire span. In this method, the entire span of the beam is supported by the wall below the beam, and in addition the beam ends are connected to the columns at the ends of the beam.
One implication in my opinion is the load transfer path of the loads to the foundation. Instead of the load path being Roof-->beam-->column-->foundation, the load path is now beam->wall below the beam-->grade beam-->foundation. As a result of modified load path, the grade beam is loaded more than the design load.
Are there any seismic implications due to this construction method? I would assume the entire wall+beam act as a single unit, thereby failing the weak beam-strong column concept.
Are there any other negatives/positives with this method? Me being a mechanical engineer could not come up with other issues. There is no structural engineer to ask this question, so here I am.
1
u/EEGilbertoCarlos 2d ago
You're describing confined masonry, not reinforced concrete.
0
u/touchable 2d ago
Your concern is valid, and yes there are definitely seismic implications.
The system you're describing will probably end up behaving as some sort of hybrid between a moment frame system and a shear wall system in an earthquake. The problem with this is that the walls likely aren't actually being designed as seismic shear walls due to the presence of the beams and columns.
It's very hard to say exactly how that type of hybrid system will behave without some advanced FEM analysis, which I doubt is being done for these buildings. That doesn't necessarily mean the building will fail, as there seems to be some inherently built-in redundancy, but I would highly recommend finding a local structural engineer to review it.