r/StructuralEngineering • • 3d ago

Steel Design Structural engineer gave us incorrect drawings

Hi guys,

Just want to know where to stand with this.

Our structural engineer has supplied us with a drawing with a steel beam that was thinner than the wall we are holding up above. For context ( 230mm wall thickness beam was 102mm)

I raised this over the phone he said it’s all fine it’s a narrow beam. My builder said he hasn’t seen anything like this & said to get this confirmed.

I wrote an email to him about the concerns & he said he’ll come down.

I already paid for a site visit, drawing & a report from him already.

Once he came down he was confused at the wall depth & said just get another beam. He left quickly after.

I’ve got a revised drawing however the freeholder/alteration team has said you will need another license to alter. This will delay us further 2-4 weeks (another mortgage payment) & additional legal fees for the license to alter.

The revised drawing has 2x UB he originally put in his drawings

What position are we in & what can we do.

I’ve raised it with him & sent him an email.

He’s a chartered engineer with his own company.

0 Upvotes

45 comments sorted by

48

u/Upset_Practice_5700 3d ago

Is he an engineer or a surveyor?

Engineers make mistakes. Not sure you can sue him for damages, does not look like there are any, regardless, not worth trying (In my opinion, however lawyers and insurance peeps may disagree.)

Surveyors should not give you steel beam sizes.

7

u/Fivefortyi 3d ago

Engineer, apologies corrected the above

10

u/Old-Slip-1319 3d ago

Can you add a 230mm wide plate to the top of the beam?

3

u/Fivefortyi 3d ago edited 3d ago

Possibly but was not specified, his response was to add another beam & sent me the same drawing except with 2x UB

11

u/TheDaywa1ker P.E./S.E. 2d ago

If you needed 2 beams to start with you arent going to get a free beam because he didnt show it initially. Thats called betterment

Realistically youre going to get him to not charge you for this additional work and thats probably it

16

u/chopperbiy 2d ago

You are not going to get any costs towards your additional mortgage costs and additional licence costs if that’s what you are thinking. It doesn’t work that way in this part of the world relative to the USA. It would cost you more to go after him than you would get back.

However I wouldn’t be paying him for any rework above his original fee.

13

u/Worried_Let4942 3d ago

Usually you’ll be ok to weld a plate to the top of it. I’d get him to alter his drawings to show that.

3

u/SelfSufficientHub 3d ago

What outcome are you hoping for?

0

u/[deleted] 3d ago

[deleted] — view deleted comment

9

u/SelfSufficientHub 3d ago

Probably not but it’s hard to say based on the op.

You wrote -
“Once he came down he was confused at the wall depth & said just get another beam. He left quickly after.”

I find it hard to imagine a scenario where a professional comes to your house, sees the issue and literally just says “just get another beam” then rushes out the door.

If it happened exactly how you described then I don’t know what to tell you- that’s a crazy fucking interaction between two humans.

Therefore I suspect it’s not exactly as you describe.

Either way you need to either have a conversation with a lawyer and tell them in detail about the incident and let them advise you or move on.

1

u/Fivefortyi 3d ago

I was just as shocked, he added the same beam in the drawing & reissued. Was here to check the wall & left very quickly.

Yeah I will do.

3

u/imissbrendanfraser 2d ago edited 2d ago

Why was he surprised at the depth of the wall? Ie why didn’t he know the depth of the wall initially and could it have reasonably been foreseen?

-11

u/Bobsaget86 3d ago

Tell him exactly the same anguish you've expressed to us here:

"Hey pal, this is your screw up (undersized beam). I need this fixed at YOUR cost otherwise I'm taking this upstairs."

He doesn't want any issues and he'll eat the cost of his mistake.

7

u/logic_boy 3d ago

It’s a little tricky, if it was a internal lodbearing wall, it’s not always obvious that a wall is double brick. It’s sometimes logical to allow for “confirmed on site by contractor” in order to progress with the works. Amendments to plans happen often and it’s not neccesarily the engineers fault.

1

u/Fivefortyi 2d ago

Yeah I think this is the answer, you are right. The freeholder doesn’t understand this. Thank you

2

u/SquirrelFluffy 2d ago

My pet peeve is when the architect goes out to try to figure out the existing structural, and then we do the design, and once we start on site it's all different. Then the client wonders why they're paying more for a redesign.

1

u/logic_boy 2d ago

That’s a classic. I do try my best to survey during a site visit, and advise if there is something crazy wrong. In cases where assumptions can have wildly different structural solutions, we’d insist on invasive inspection. But in case of a single/double beam, it’s quite a minor difference tbh.

2

u/SquirrelFluffy 2d ago

The issue I'm pointing out, and it seems you confirmed it, is that the architect doesn't understand what minor structural issues are. Oh it's no big deal if the joists run the other way! Yeah because now you've got your bearing walls and lateral loads in a different place. Easy.

Extra beam that weighs 500lbs? Easy for the contractor. Owner can pay!

1

u/logic_boy 2d ago

Yeah totally agree

8

u/September1752 3d ago

Is he a chartered surveyor or a chartered engineer? A surveyor shouldn't be specifying beam sizes.

4

u/EngineerEngineerEngi 3d ago

TIL that England calls a licensed engineer a "chartered engineer".

14

u/PinItYouFairy CEng MICE 2d ago

Chartered Engineer is a protected title and is capitalised. Chartership is granted by meeting the requirements of the Engineering Council, and usually happens at the same time as meeting the requirements of a Chartered Institute (like the Institution of Civil Engineers https://www.ice.org.uk , or Institute of Structural Engineering https://www.istructe.org)

It is subtly different from being a professional engineer, as it’s recognised country (and world) wide.

Becoming chartered means you have demonstrated a standard set of abilities broadly aligned with you being able to function competently, professionally and responsibility. It does not imply, necessarily, that you are the best engineer in the world.

Finally, chartership permits the individual to use CEng post noniminals, and membership of a chartered institute permits further postnoms; MICE for member of the institution of Civil Engineers and MIStructE for Structural Engineering.

Hope that is helpful/interesting

2

u/EngineerEngineerEngi 2d ago

That is interesting, thank you.

I just looked up some comparisons of US -> UK, does this look correct?

  • Certified Engineering Technician -> Engineering Technician
  • Engineering Technologist -> Incorporated Engineer
  • Engineer in Training/Intern -> Graduate/Associate
  • Professional Engineer -> Chartered Engineer
  • Structural Engineer -> Fellow/Supervising Civil Engineer

5

u/PinItYouFairy CEng MICE 2d ago

I’m not sure, but “structural engineer” is a type of engineer focussed on structures, instead of civil engineering which is more broadly the “built environment”

So your last point is incorrect. It’s a specialism, like being a “bridge engineer” or “dams and rivers engineering”

1

u/SquirrelFluffy 2d ago

Not quite. Prof engineer = Prof engineer.

Chartered engineer = certificate of authority in USA CofA in Canada. License to provide services to the public, as opposed to working for someone.

1

u/EngineerEngineerEngi 2d ago

Canada? I thought "chartered engineer" was a UK thing.

1

u/SquirrelFluffy 2d ago

I just mentioned the c of a in Canada because I'm Canadian. And hold the c of a

1

u/Most_Moose_2637 2d ago

Not really. Incorporated engineer is still an engineer but tends to be one without a masters degree. You have to have the equivalent of a masters to be chartered in the ICE or IStructE.

Incorporated engineer has completed most of the professional requirements of being chartered but would have to either gain their masters or go through a career appraisal or technical report route.

3

u/ReplyInside782 2d ago

Weld a wider plate on top of the beam have the engineer detail it for you. If the beam itself is fine, then adding a plate shouldn’t be an issue

2

u/imissbrendanfraser 2d ago edited 2d ago

Sounds like the beam was designed for 1 leaf so now that there’s possibly two leaves, it could be double the load and it’d need the two beams

1

u/Objective_Two_5467 3d ago

Your wall is 9 inches thick? Is it masonry?

1

u/Fivefortyi 3d ago

Yes, It is masonry

-6

u/Old-Slip-1319 3d ago

A 4" wide beam (not sure of depth) seems undersized to support a cmu wall. You should have this checked by a structural engineer.

7

u/Fantastic-Counter927 3d ago

All depends on depth load and span. 

-2

u/Old-Slip-1319 3d ago

Well yeah.

2

u/imissbrendanfraser 2d ago

2No. 102mm wide beams will support 2No. 102mm thick leaves of brick. Assuming that’s what we’re dealing with but OP hasn’t provided much context, however they have clarified that it was an structural engineer, not a surveyor.

1

u/Old-Slip-1319 2d ago

Yes. I'm also happy Brendan Fraser it back too BTW.

1

u/pina59 3d ago

At 102mm wide it's either a 178,203 or 254 depth. This sounds like a residential project, in which case a doubled 178 would typically be acceptable for that thickness of wall

@op, you need to check what the appointment and scope was with your engineer. You should be asking for a revised drawing indicating the change and revised details. Typical in this case is 2 beams with a top plate welded on in a hit and miss pattern.

0

u/Fivefortyi 3d ago

Agreed. He has now said to use 2x the original
beam & bolt them together

4

u/SquirrelFluffy 2d ago

Did the engineer do their design working off an architect's plan? Because it may not have properly showed that wall as double wythe masonry.

1

u/JG300192 2d ago

Firstly, please do not take remedial advice from the posts on here, we have no context on the length of the new beam, the height of the wall it is supporting, if it is an internal or external wall, how many floors / roof does it support etc.

The information is very limited in this post for people to be providing structural solutions.

I presume it is a solid 230mm rather than a cavity construction. I suspect the 2 no. beams side by side is the correct approach, but the incumbent engineer needs to provide the structural calculations.

I don’t understand why you need to undertake a new application unless your current application expired or you are undertaking new / additional works not shown on the original application. Is one of these scenarios applicable? In either case I think you’d struggle to attribute this as the engineer’s fault.

Based on what I can glean from here. All I can advise here is that the engineer should not charge you for additional works / drawings to account for the extra beam. Providing the proposed alterations have remained the same throughout this process, I’d also question the freeholder on why a new application is required. The only additional cost should be the material and labour for 1 no. Additional beam from the contractor.

1

u/Superb_Sea7721 1d ago

From the steel side, two beams side by side under a 9" masonry wall is about as routine as it gets, so the fix itself isn't a big deal. What I'd check on the revised drawing is how the two beams are tied together. They need bolts with spacers or packers at regular spacing so they work as one member, plus bearing details at each end. That's the first thing a fabricator will ask about, and if it isn't on the drawing you'll lose more days to back-and-forth. On the money, I wouldn't chase him for the delay, but I'd ask in writing that the revision and any extra site visit are at no charge, since the first design didn't fit the wall it was holding up.

1

u/CAGlazingEng 1d ago

A little late to the conversation but are you not working off of drawings? I know residential is a little more fast and loose with detailing. What was he working off of and what did you ultimately get?

1

u/ronfnma 4m ago

Add a second beam with a 26 mm gap between them so the out to out dimension equals the width of the wall

0

u/ExcelEng 2d ago

This is crazy. It would’ve taken him two minutes to give you another option for a beam. Not sure why he did not do that.