I bet. Especially since I dont do them. Im coming up with hip that is double 12" LVL's, yet I look at some other designs, or pictures and there is a 2x10 shown.
No. No. The ceiling framing does all the work. Add ceiling beams to control joist spans. Spec strongbacks to control rafter spans. Ridges hips and valleys braced every 4ft. All rafter loads braced to beams or load bearing walls
There are charts for the rafter and rafter ties in the IBC. You can use almost any software for the rafters and ridge beam. It isn’t really that much different in terms of effort than designing floor joists.
I get component design, I guess I am looking at a hip with a 2500 lb reaction, connecting to a ridge that has no post. Or are you posting down every ridge/hip beam end?
The hip beams can (and should) have intermediate supports. I usually specify a roof brace (vertical or slanted a small degree) at regular intervals. The roof brace would bear on a post embedded in a stud wall or a ceiling beam. Roof braces would similarly support ridge lines, valleys, purlins, etc at regular intervals.
Lol. No the framer places a 2x10 plate under the whole connection and braces that down to an approved load point. Draw a circle at the connection on plan and arrow it to the plan you want it braced to. Don't exceed the code max angle. The brace length matters and is typically detailed as two opposed 90 degree 2x6s
Indeed lots of posts. But they should already be there per code - only difference is now you are designing them.
Code is very weird, the baseline stick framing in code is reliant on thrust detailing via ceiling joist/rafter tie connections to rafters, and it treats hips, ridges, and valleys as all non-structural (with pitch >3:12). Yet, it requires braces to bearing walls at their ends (which would not make sense if they are non-structural). From an engineering perspective, valleys should always be structural, but hips and ridges could be non-structural with appropriate thrust detailing (for pitches >3:12).
So there’s 2 ways to approach a roof like this IMO: 1. Design the ridges and hips as non-structural where that’s possible, and ensure the thrust detailing is adequate 2. Say screw that because thrust detailing is annoying when you have different ceiling joist and rafter spans everywhere and design everything as structural instead.
Build cost difference won’t be crazy
By the way, im assuming this isn’t a heavy snow load area
What particularly are you finding difficult for this design. Might help answering your question. Wood framed resi is mainly what I do, might be able to assist.
Mainly where supports would go for the ridges and hips or am I relying on them acting as beam columns and just design as simple beams along their lengths?
I’ve done roofs like this plenty of times. They suck haha. Are you in US / canada? ForteWeb is the place to start. Dm me if you have any specific questions.
I have been using forteweb. So, for instance, this corner of my actual project, the hip I was getting a 7.25" LVL (I can post down near middle) and then at the top I was going to have a post at the end of the ridge to support the end and the other small hip.
Now that is causing me to need a LVL in the ceiling to support the post. I would assume I would need a post at the valley end too.
Yes that’s generally how I do it as well. I try to support mostly with ridge beams because they’re easier to do a strong connection (ccq) to a king post. Sometimes I’ll cantilever the end of the ridge to allow space for the hip / valley connection. And sometimes I’ll need the intermediate hip/valley support like you’ve shown. Ceiling beams supporting the king posts can get huge if they need to span between exterior walls, and then you have to check the sloped notch in the ceiling beams at the exterior walls. Also try to use heavier brackets for king posts to beams and ceiling beams (upside down caps), since they have no sheathing to brace them.
Generally unless there's a vaulted ceiling or something where I'm using the rafters as the ceiling support as well I size the ridges and hip/valleys so I can post down about every 8'. I wouldn't do them as simple spans unless the ceiling conditions demand that. Going to end up way over sized. Those pitches make it a lot easier to get more supports to walls saving money on beams in the ceilings. Supports are cheap so if you need more supports to keep your member sizes down add 'em. I'm guessing this is single story, at least from the exterior? Keep it simple contractors won't be wanting to change member sizes more than they need to. Find your worst case scenarios and if they are reasonable sizes use that throughout.
Thanks. The picture I posted is not my actual project, but represents some of the complexity. I didnt want to post the actual drawings. There is a second story portion in the middle, so there are walls I Can post to. Rest to the outside is just open attic area down to ceiling joists
Got ya. Wasn't sure if it was just a stripped down version.
Remember when you get those high pitches you might be able to span supports pretty far to walls instead of ceiling without the angle of the support actually being too steep. Sometimes that isn't intuitive when looking at it in plan view. Saw someone else say forteweb for software. I second that. Feel free to DM me.
I feel your pain. Doing a roof for a 20k square foot house like this, just bigger. Builder is old school and wants to do it stick framed. Just make your ridges, hips, valleys structural with purlin braces to break up rafter spans.
Forteweb software is great for this kind of thing since you can link reactions. That way if you update something it carries down the line following the load path.
We have a perpetual debate in our office whether the ridges of hip roofs need posts down to a beam in the ceiling. If the pitch is steep enough I believe you can get away with it being a non structural ridge. Framers I've talked to say the important thing is to keep a common rafter right at the end of the ridge regardless of how 16" of falls taken from the corners of the building. And good tights cuts on the beveled plumb cuts of jack rafters. So you might want to show that common explicitly aligned with the ridge.
I had an inquiry like this before the pandemic. I actually entertained it for a week or so. Until the client said he wanted full open span cathedral ceilings on the top floors. No walls.
Based on the column layout and structural details provided in the image, I would like expert recommendations regarding the beam design for this G+2 building.
Considering the following:
Building dimensions: 60 × 68 ft
Column spacing: 17 ft along the 68-ft direction and 20 ft along the 60-ft direction
Three middle columns arranged in one straight line
The central girder is supported by the three middle columns, while both ends of the girder are intended to rest on the walls on either side.
All columns: 18″ × 18″
Column reinforcement: 4 × 20 mm + 8 × 16 mm
Floor-to-floor height: 15 ft
Steel grade: Fe 550D
Slab thickness: 6 inches
Wall thickness: 9 inches
Foundation: Isolated footings
Area in square yards Approximately 453.33 sq yd
My questions are:
What should be the appropriate beam width and depth for the different spans in this structural arrangement?
What should be the required top and bottom reinforcement (number and diameter of bars) for each beam?
What stirrup diameter and spacing should be provided, particularly near beam-column joints?
What is the appropriate and economical beam arrangement for this structure without compromising structural safety?
[ Considering the central girder is supported by three middle columns and its two ends are intended to rest on the side walls, is this support arrangement structurally feasible for a G+2 building, and what would be required to design it safely? ] <<<
I am willing to provide any additional information, drawings, photographs, structural details or site-related information if anyone is interested in reviewing this project or helping me find a technically sound and economical solution. I would genuinely appreciate guidance from experienced structural engineers and professionals.
If i need to add a post to reduce the clear span of a hip, i design a beefed up ceiling beam with a point load wherever the post is that matches the end reaction of the reduced hip span. Same thing for any ridges that are supporting hips. Of course that’s the last case if i cant post anywhere else like a bearing wall. Obviously it depends on the layout and orientation of everything, where the bearing walls are, etc.
20
u/kc_ky 2d ago
The framers will hate how you detail it, guaranteed.
9
u/OptionsRntMe P.E. 2d ago
I hate roofs like this. Yes it’s possible. No it’s not fun or efficient
4
u/Ddd1108 P.E. 2d ago
Are talking rafter ties and ridge board? Or rafters and ridge beam?
7
u/Crawfish1997 2d ago
For a super complex roof like this, just design everything as structural - ridges, valleys, and hips. I wouldn’t bother relying on thrust detailing.
3
u/fractal2 P.E. 2d ago
What particularly are you finding difficult for this design. Might help answering your question. Wood framed resi is mainly what I do, might be able to assist.
1
u/Pilotdoctorengineer 2d ago
I feel your pain. Doing a roof for a 20k square foot house like this, just bigger. Builder is old school and wants to do it stick framed. Just make your ridges, hips, valleys structural with purlin braces to break up rafter spans.
1
u/PE_Structural 2d ago
I never understand entirely, it’s not efficient in anyway…props to the guys framing, but their bid will increase substantially because of it.
1
u/Turkey_Processor 2d ago
Forteweb software is great for this kind of thing since you can link reactions. That way if you update something it carries down the line following the load path.
We have a perpetual debate in our office whether the ridges of hip roofs need posts down to a beam in the ceiling. If the pitch is steep enough I believe you can get away with it being a non structural ridge. Framers I've talked to say the important thing is to keep a common rafter right at the end of the ridge regardless of how 16" of falls taken from the corners of the building. And good tights cuts on the beveled plumb cuts of jack rafters. So you might want to show that common explicitly aligned with the ridge.
1
u/WL661-410-Eng P.E. 2d ago
I had an inquiry like this before the pandemic. I actually entertained it for a week or so. Until the client said he wanted full open span cathedral ceilings on the top floors. No walls.
1
u/DadwalGurkirat 13h ago
Beam Design and Reinforcement Requirements
Based on the column layout and structural details provided in the image, I would like expert recommendations regarding the beam design for this G+2 building.
Considering the following:
Building dimensions: 60 × 68 ft
Column spacing: 17 ft along the 68-ft direction and 20 ft along the 60-ft direction
Three middle columns arranged in one straight line
The central girder is supported by the three middle columns, while both ends of the girder are intended to rest on the walls on either side.
All columns: 18″ × 18″
Column reinforcement: 4 × 20 mm + 8 × 16 mm
Floor-to-floor height: 15 ft
Steel grade: Fe 550D
Slab thickness: 6 inches
Wall thickness: 9 inches
Foundation: Isolated footings
Area in square yards Approximately 453.33 sq yd
My questions are:
What should be the appropriate beam width and depth for the different spans in this structural arrangement?
What should be the required top and bottom reinforcement (number and diameter of bars) for each beam?
What stirrup diameter and spacing should be provided, particularly near beam-column joints?
What is the appropriate and economical beam arrangement for this structure without compromising structural safety?
I am willing to provide any additional information, drawings, photographs, structural details or site-related information if anyone is interested in reviewing this project or helping me find a technically sound and economical solution. I would genuinely appreciate guidance from experienced structural engineers and professionals.
0
u/TaroExpensive 1d ago
That's not a big roof. What's the big deal? Stick frame it.
-1
u/ajs263 2d ago
Of course you can do it by hand. Roofs have been engineered long before software to do it.
0
u/Real_Sociopath 2d ago
If i need to add a post to reduce the clear span of a hip, i design a beefed up ceiling beam with a point load wherever the post is that matches the end reaction of the reduced hip span. Same thing for any ridges that are supporting hips. Of course that’s the last case if i cant post anywhere else like a bearing wall. Obviously it depends on the layout and orientation of everything, where the bearing walls are, etc.