Structural Analysis/Design Concentrated Load on Slab
- Suspended slab with band beams, assume simple
- 8m slab span (centre to centre)
- 1500mm wide band beams both ends
- 2x 90 kN point loads mid span, 2m apart transverse to span direction
AS3600 provides guidance on the effective moment resisting width (beff), works out to be just over 4m.
beff will overlap, how have you all dealt with this?
3
Upvotes
5
u/egg1s P.E. 2d ago
I don’t fully understand your terminology here, but if the beff overlap, I’d just take the actual beff only to the point where the two sides meet, seems like a conservative assumption.
2
u/spiritladder 1d ago
RAM concept would give you the best answer, but assuming you are doing it in something like RAPT the most conservative way would be to use a 2m wide strip only (1m being the width before the loads begin to overlap - i.e. you choose two strip widths such that there is no overlap and the load is central to the strip). May not work though.
You could also potentially check it as 180kN acting on a wider strip, although the central zone will be more stressed.
There may be information in other codes about design strip widths with closely spaced loads (perhaps FIB model code).
Punching may be an issue, and you need reo in the secondary direction, which the code doesn't explicitly tell you how to calculate.
1
u/koy_boy996 2d ago
They can overlap just take the overlapped width, not 2xbef.
The commentary states you need a minimum amount of transverse reinforcement to distribute the load across the strip which is not less than half the longitudinal reinforcement.
If you have P/A from post-tensioning in the transverse direction you can use this to minimise the reinforcement required.
1
u/bridges_355 2d ago
I don't believe it matters that beff overlaps. You get a moment from the two point loads (if i understand correctly, 90kN x 3m = 270kNm), and you have a beff to resist it.
Check in RAPT
You also should check punching shear capacity, especially if the slab is green (freshly poured, maybe only 25MPa if this is a construction load from a prop or something).
0
u/Marus1 1d ago
You see, this is the issue if you teach people a theoretical approach and not let them understand the practicalities behind it