r/StructuralEngineering • • 2d ago

Structural Analysis/Design Concentrated Load on Slab

- Suspended slab with band beams, assume simple
- 8m slab span (centre to centre)
- 1500mm wide band beams both ends
- 2x 90 kN point loads mid span, 2m apart transverse to span direction

AS3600 provides guidance on the effective moment resisting width (beff), works out to be just over 4m.

beff will overlap, how have you all dealt with this?

3 Upvotes

14 comments sorted by

5

u/egg1s P.E. 2d ago

I don’t fully understand your terminology here, but if the beff overlap, I’d just take the actual beff only to the point where the two sides meet, seems like a conservative assumption.

1

u/Western-Phase-9070 1d ago

Potentially, but the overlap will see double the moment intensity so maybe not conservative

1

u/egg1s P.E. 1d ago

But if your beams work with the smaller beff, then the load won’t need to spread into the overlap.

2

u/spiritladder 1d ago

RAM concept would give you the best answer, but assuming you are doing it in something like RAPT the most conservative way would be to use a 2m wide strip only (1m being the width before the loads begin to overlap - i.e. you choose two strip widths such that there is no overlap and the load is central to the strip). May not work though.

You could also potentially check it as 180kN acting on a wider strip, although the central zone will be more stressed.

There may be information in other codes about design strip widths with closely spaced loads (perhaps FIB model code).

Punching may be an issue, and you need reo in the secondary direction, which the code doesn't explicitly tell you how to calculate.

1

u/Western-Phase-9070 1d ago

Excellent, thank you. Checked other codes that I have access to, more info on minimum steel in transverse direction but not much on overlapping regions, perhaps I have over thought it.

1

u/spiritladder 1d ago

Tinking further I think the way to do it would actually be to convert the point loads into 2x UDL's acting in the transverse direction, perpendicular to span (as this is essentially what the equivalent width in the code is doing, saying you have beff of cross section resisting a point load uniformly). Then in the overlapped area transform this to an equivalent load, acting on a strip of width equal to the overlapped area. And then check the "central" strip, and the "edge" strips separately.

E.g. if each pt load has a 4m wide strip and the pt loads are 2m apart, you have a 2m wide overlapping zone, lets call it the "central strip", which carries 50% of each point load, and 2x 2m wide "edge strips" which carries 50% of each load. Given your dims, the central 2m strip will carry 50% of both, i.e. a "central strip" of 2m strip carrying 90kN, and 2x "edge strips" of 2m, each carrying 45kN. Design for the central strip and use that reo/PT everywhere in this zone.

1

u/koy_boy996 2d ago

They can overlap just take the overlapped width, not 2xbef.
The commentary states you need a minimum amount of transverse reinforcement to distribute the load across the strip which is not less than half the longitudinal reinforcement.
If you have P/A from post-tensioning in the transverse direction you can use this to minimise the reinforcement required.

1

u/Western-Phase-9070 1d ago

Potentially over conservative? Ignoring the rest of beff

1

u/bridges_355 2d ago

I don't believe it matters that beff overlaps. You get a moment from the two point loads (if i understand correctly, 90kN x 3m = 270kNm), and you have a beff to resist it.

Check in RAPT

You also should check punching shear capacity, especially if the slab is green (freshly poured, maybe only 25MPa if this is a construction load from a prop or something).

1

u/Western-Phase-9070 1d ago

True, might be a case of over thinking.

beff from the Australian concrete code FYI

0

u/NoMaximum721 2d ago

What are you calling beff if you're taking the moment from both point loads at once? (I'm not familiar with euro code but I'm assuming this is an effective resisting width?) 

1

u/bridges_355 2d ago

There's a calc in AS3600 for the slab width engaged from a point load. From memory, it's based on point load distance to support.

0

u/Marus1 1d ago

You see, this is the issue if you teach people a theoretical approach and not let them understand the practicalities behind it

0

u/Western-Phase-9070 5h ago

Should I load test the slab until collapse to figure out the beff? That’d be pretty practical, but might be easier to theoretically calculate it.

Can’t believe you took the time to write such a useless response 😂