r/accesscontrol • u/MIDNIGHTBLISS98 • 3d ago
Onguard; Different facility code on reader
We programmed the access cards already all are fine except one reader that reads a separate facility code on Onguard, any way to change that so the reader picks up the card? The cards have a different facility code than that one reader. The master panel is a LENEL S2 LNL-M2220 I’m using Onguard. Any spitballs my way would be appreciated
3
Upvotes
5
u/MIDNIGHTBLISS98 3d ago
Thanks for the help yall, I fixed the issue by swapping the green n white cables on the panel itself,
4
u/ApolloFett 3d ago
Check that the correct card format is enabled for that reader
3
u/sryan2k1 3d ago
What readers? What mode? If it's wiegand did someone flip D0 and D1?
2
u/Prof_plum_1234 3d ago
The problem is on one reader. Don't modify the card format you have a single device issue. It's likely reading the correct number of bits and your data is around the wrong way, like contributor already said. Take the reader to the DRI and wire it to the terminal block. Present card. Log finding. Hot plug terminal block to a working reader slot. Present same card. Log finding. Compare. Draw conclusion. Line fault, reader fault, configuration fault.