I upgraded from an EP1501 to an MP1501. I moved the standoffs over and the board powers-up and can read a card, but when an input fires the board resets. I feel like there's an inrush of voltage causing it. I put a meter on it and got 4v at the "dry" contact so I'm not sure where that voltage is coming from. Its getting PoE+ from the switch. Anyone seen this before? There's no lock, only door contact.

3 Upvotes

16 comments sorted by

3

u/PatMcBawlz 7d ago

Sounds like you are shorting a power supply. Pull off all the field wiring (except the network / poe) and re-run your tests.

1

u/Shakarix 7d ago

Sorry meant to say there was only a door contact. No lock. PoE only.

1

u/csking77 7d ago

When the input “fires”, does that mean when the input closes? What type of input signal are you using, just the dps and resistor, maybe?

1

u/Shakarix 7d ago

Yes its normally open. There's no resistor. There's an LED that goes to VO that goes on the other side of the door. If I just wire two wires together without the LED it works fine.

3

u/csking77 7d ago

I don’t fully understand the LED and VO that you are describing, but there should be no “additional” power on the inputs. If, for some reason you need power on the device that interfaces with your input, you will need to use a relay to isolate that power from your inputs.

-1

u/Shakarix 7d ago

The EP board did it no problem.

4

u/PatMcBawlz 7d ago

What? You shouldn’t be running power to input terminals.

1

u/OGDukeFlapjack 3d ago

If you're still having issues what happens if you remove the board from the standoffs and just let it hang? Are they metal or vinyl? I've had boards sometimes behave very erratically if they're getting transient voltage through the back box.

1

u/Shakarix 3d ago

If I take the standoffs off and power cycle, it comes back online. I'm just going to have to take away the VO thing.

1

u/OGDukeFlapjack 3d ago

What's the wattage of the PoE? I reread your post and the voltage you metered made me think. You should be metering somewhere around 5vdc I think. Your PoE may be under amped. I'd recommend at least 30-watts. Some switches have issues with Mercury PoE and don't automatically set the wattage right.

As an aside, I don't know if you knew this but you can tell the state of an input based on the voltage you meter. If it's zero (and you have power, obviously) the input is shorted. If it's 5-ish volts it's open. If it's in between it has a resister on the circuit. Bosch security specifically prints this on their panels.

EDIT: PoE can absolutely give enough amperage to operate a door. I've run an entire reader/REX/strike off of the output voltage on a PoE driven 1501. They don't output a lot but they can work.

1

u/Shakarix 3d ago

Its connected to a PoE+ switch and the board verifies it. When the circuit is open its 4v.

1

u/OGDukeFlapjack 3d ago

I'm not sure what the voltage is supposed to be so I'm going to assume it's normal. So does the door operate normally when it's not connected to the standoffs or does it continue to do the reset thing?

1

u/Shakarix 3d ago

Only when the circuit closes does it reset

2

u/jc31107 Verified Pro 7d ago

Inputs have voltage on them, normally either 3.3 or 5vdc open circuit. The board uses the voltage to measure resistance on the circuit with a fixed current. This is how is can tell open/short/1k/2k

I’m a little confused when you say there is an LED going to V0. Can you upload a quick and dirty sketch of what you’re doing.

You can’t really drive anything off the input voltage, and shouldn’t be connecting anything to V0 on the board. The input is pulled high with an internal resistor and then the field wiring pulls it back to ground when it’s active

1

u/rsgmodelworks 4d ago

make sure your PoE source is serving enough power and it is the proper type?