Installing

Hi smart people. I had a guys try to change my thermostat honeywell to ecobee but its not turning on. The ecobee is just blank. So he said no voltage on blue wire so we put back the honeywell. I have a new build the builder said thats odd because it should have one. Here is the pic the guy took.

So what was the problem and can I just do it myself?

0 Upvotes

7 comments sorted by

2

u/geekywarrior 6d ago

Should work if the fuse wasn't blown. Possible that blue isn't tied in at the handler though.

1

u/DisastrousAd4287 6d ago

This was my problem. I had a Honeywell thermostat with batteries prior to the ecobee, so the voltage from the common was not needed. When I installed the ecobee it wouldn't come on. I checked at the handler, the blue (common) was disconnected. Once connected, the ecobee worked.

2

u/CertainAttention6749 6d ago

Check your furnace/hvac control board to verify if blue wire was connected toc slot. Your honeywell might not have wifi feature so continuous power is not required. Going back to control board, in case blue wire isn't connected, turn hvac power off before attempting to connect blue wire to c slot. Good luck 👍

2

u/Revzerksies 6d ago

I would suspect that the C wire does not have power or ever had it

1

u/Feisty_Raccoon_688 6d ago

I know this is an example of 1, when I did mine 6-7 years ago the blue wire was not connected on either end. Not on the old thermostat, not on the furnace. I would check check / check ed that the furnace it actually producing the 24V across the appropriate poles.

Is your old thermostat battery powered or should be powered by the furnace.? In my case it was one of those builder specials, with 3 AAs.

1

u/NewtoQM8 6d ago edited 6d ago

Like geekywarrior said, if the Honeywell was battery operated there's a good chance C isn't connected at the control board end, or that the fuse on the board is blown, or the cover wasn't put back on properly (They usually have a switch that cuts power to the thermostat) or the circuit breaker is off. You can measure for AC voltage at the thermostat end between RC and C. If no voltage check between RC and G, if it has voltage it means the C isn't connected. If neither its a blown fuse or cover switch.

0

u/itsallahoaxbud 6d ago

Have you called ecobee support? They are extremely knowledgeable and will do everything possible to help you.