r/electrical • • 1d ago

Quick question

Post image

Hey guys.

I have a three gang switch at my entryway wired exactly like this. The left switch, has always been hooked up but it never actually turned anything on which has been weird but I lived with it. The middle switch is for the entry ceiling light and the right switch is for the exterior soffit lights.

The other day, my wife bumped into the wall next to the switches and all the lights went out. I checked the breaker and nothing was tripped. I ended up switching out the old metal three gang box for an old work blue box and installed three new Lutron switches. However, the lights still aren’t working. I flipped every switch on the breaker panel just in case and the lights still aren’t working. Has anyone seen this before and have any solutions? Just checking before I start cutting into walls to trace the romex for shorts or other issues.

1 Upvotes

9 comments sorted by

3

u/Particular_Week_2754 1d ago

What does your voltmeter tell you when you measure the voltage at your incoming power cable? Once you establish that, we can move onto next step of the troubleshooting.

2

u/jakedouthat 1d ago

I unfortunately don’t have access to a volt meter tonight but my non contact tester pen is showing the incoming power hot (red light and beeping), then when they’re hooked up to the switches, everything is hot (according to the tester pen). I even tried switching out a working ceiling fixture at the entryway and that’s not working either.

Guess I need to go get a volt meter tomorrow to test that incoming power

1

u/Particular_Week_2754 1d ago

I would recommend getting a voltmeter for more assertive testing. It will also help to establish present neutral connection.

If the incoming voltage is present between the line and neutral wires, then the possible problem is going to within connections at the box, wiring downstream, or fixtures themselves. I lean to believe it’s wiring within the box.

Since you mentioned replacing the box, it means you redone all of the connections. I would confirm the correct state of those before any additional steps.

Make sure incoming neutral is connected with the lights neutrals. You can remove switches to make it more simple and eliminate possible switch problems.

Once you confirm that all neutrals have been connected, connect incoming line to one of the outgoing switch legs. If the light doesn’t turn on, remove the fixture and test for voltage between hot and neutral, using voltmeter. If it reads 120, you have a bad light.

1

u/Acceptable_Sky_9742 1d ago

Do you have power on the neutral? Is there anything else on the circuit that you can turn on and confirm is on, and then test the neutral for power? If the hots are all hot, my guess is that the problem is with the neutral. Do you know how the cable gets into the box? Does it come from a receptacle? Does that receptacle work? Could be a problem with the neutral at or between the last working device and this junction box.

4

u/Reddic1 1d ago

Check for any tripped GFCI receptacles first if none of the breakers are tripping

3

u/jerpvtx 1d ago

Simple, easy test: get the switches out of the equation. Turn breaker off, connect incoming hot, neutral ground directly to one of the lights turn breaker on, see if light goes on. Then you know if source wiring is good or bad.

1

u/Ok_Patience1542 1d ago

That 3rd switch probably controls half a plug. If the top and bottom of all your plugs are always on, one of them maybe have been replaced amd the tab between top and bottom was never broken off, or they just didnt hook up the extra wire from the switch.

0

u/Patient-Big1727 1d ago

You can't do real troubleshooting without a multimeter. Where is the left hot wire going? Why would you connect power to a switch that doesn't control anything?

A wild guess is that the bump caused contact and arcing either of the unknown hot wire or a hot touching the box. The power draw from that could have caused a loose connection to arc and completely loose connection. Make sure all wire nuts and screw connections are torqued appropriately. Check for evidence of excessive heat. You gotta work through that circuit from end to end

0

u/Neon_Synchronicity 1d ago

I am following the clue that your wife bumped the switches and the lights went out. All of those switches appear to be single pole (line/power to the switch and load/power out). In a 3 gang box like that, there is commonly 1 line wire to the box, all grounds are tied, all neutrals are tied, and the line is pigtailed to the bottom of each switch. Shut power to this location off. I would check all of your connections. Be sure connections to the switches are wrapped around the screws tightly on the sides. Look at your hot and neutrals. I usually take the wire nut off to see that the ends were twisted with line pliers as opposed to just placed together relying on the wire nut to fasten. If you check all that, turn it on and see if that fixes. If not, you may also have a bad switch/s. From there you would need to check voltage with a multi-meter.