r/electrical • u/Mr_Midwest7 • 3d ago
3 phase contactor fried itself? Help!
Recently I was tasked with getting one of our heaters ready for the winter and I was messing with it, testing the new display and control program that was installed. Everything worked fine, then it sat for a few weeks. Came back to get it fired up and the contactors weren’t pulling in. I checked everything, it was getting the proper 120v control voltage when it should’ve gotten it, and all three legs had the voltage they should, but it wasn’t working. Checked the contactors and sure enough they’re fried somehow. They’re rated for 600v 3 phase and up to 250v control, I’m running 480 and 120. Any ideas on what might’ve caused them to shit out? If I had to guess I’d say the ambient heat in the panel just cooked them over time, it averages about 65C under full load bc of it’s proximity to the heating elements and the data sheet says they’re only good for up to 70C. If I was confident in that guess I wouldn’t be asking though, so do what you will with that info.
NOTE: this is not my area of expertise so I preemptively apologize if I respond to your comments with dumbass questions and/or statements, I’m not electrically inclined and have had zero schooling on the subject.
EDIT: thanks for all the comments and advice, this has been eating at me all day. I opened it up and sure enough one of the bits on the circuit board was cooked. It wasn’t cooked in the other one but seemed to have seen some heat. Pulled the part number off the parbaked chip and it’s a variable resistor. No help to me, but might be a clue for one of you?
3
u/4eyedbuzzard 3d ago
This makes me somewhat concerned for your safety.
What exactly is fried?
Is it the 480V 3ph contacts, or the 120V contactor coil, both, melted contactor, etc?
Is the contactor rated for the current being drawn by the "heater"? (check heater nameplate and with amprobe)
Contactor for continuous duty heating equipment should be sized at 125% full load current.
Is this just resistance heating element(s) being powered or is there also a motor/blower?
How often does the contactor cycle on and off?
Does it ever chatter?
What controls the energization/deenergization of the coil?
1
u/erie11973ohio 3d ago
Are the contactors "pulling in" ?
If they are not, then the contactor coils are fried & need replaced. OR there is a control issue.
If the contactors are pulling in & no heat, then the contacts are all burnt to hell & the contacts need cleaned or replaced or the entire contactor needs replaced.
Be careful. 480 will give you a bad day! 😱😱💀💀
1
u/greenday9261 3d ago
You said the contractor coil is “rated up to 250V”.
Every contractor I’ve worked with has a single coil voltage. If you put 120V to a 208/230V coil the magnetic field will be too weak and not pull in the contacts. This will cause high amperage in the coil which heats it up and kills it.
1
u/bazilbt 3d ago
Heater resistance and amperage of the contactor?
1
u/jeenyuss90 3d ago
When you say youve got 120v. Is that 120v from a1 to a2?
Have seen it before the neutral is loose. Bringing power to the coil but no return. Most recent case was a knife on a terminal block was open.
1
u/Unique_Acadia_2099 3d ago
It does sound as though the coil is dead and there are lots of possible causes. But one of the main ones is rapid cycling, also called “chattering”. Something in your control system may be causing the contactor to turn on and off rapidly, like multiple times in the span of a few seconds. This will burn the contacts as well, but often will cause the coil to overheat, swell up and jam either open or closed. Jammed closed is an obvious disaster, but jammed open is not. Then if the controls keep trying to close it, the magnetic current stays too high until a coil wire melts inside and current stops flowing.
Control circuit chattering on something controlling heat is sometimes caused by poor design of the circuit, because they fail to include enough “hysteresis” in the command to pull in the contactor. You can’t use a simple thermostat like you might have on a direct control, meaning power goes directly from the t-stat to the elements, like on a baseboard heater, no contactor. Hysteresis means there is a “cut in” (On) and “cut out” (Off) temperature value so that the contactor is not constantly banging on and off. Someone may have not known that, or set to low. This can often happen (in my experience) when a PLC is used and the programmer is unaware of control theory from the mechanical side of things. For example I have seen it happen when they were used to using solid state heating controls like SCRs, then someone tells them to change to contactors because they are cheaper, but they don’t know that the contactor cannot turn on and off as fast as an SCR without damaging itself.
Just something to consider.
1
u/Soft_Garbage7523 3d ago
Coils fail. No particular reason. Some contactors have replaceable coils; others mean it’s a new unit…..
1
u/4eyedbuzzard 3d ago
Replying to update.
Assuming this is an AC output from a PLC or similar: