3 phase contactor fried itself? Help!

Recently I was tasked with getting one of our heaters ready for the winter and I was messing with it, testing the new display and control program that was installed. Everything worked fine, then it sat for a few weeks. Came back to get it fired up and the contactors weren’t pulling in. I checked everything, it was getting the proper 120v control voltage when it should’ve gotten it, and all three legs had the voltage they should, but it wasn’t working. Checked the contactors and sure enough they’re fried somehow. They’re rated for 600v 3 phase and up to 250v control, I’m running 480 and 120. Any ideas on what might’ve caused them to shit out? If I had to guess I’d say the ambient heat in the panel just cooked them over time, it averages about 65C under full load bc of it’s proximity to the heating elements and the data sheet says they’re only good for up to 70C. If I was confident in that guess I wouldn’t be asking though, so do what you will with that info.

NOTE: this is not my area of expertise so I preemptively apologize if I respond to your comments with dumbass questions and/or statements, I’m not electrically inclined and have had zero schooling on the subject.

EDIT: thanks for all the comments and advice, this has been eating at me all day. I opened it up and sure enough one of the bits on the circuit board was cooked. It wasn’t cooked in the other one but seemed to have seen some heat. Pulled the part number off the parbaked chip and it’s a variable resistor. No help to me, but might be a clue for one of you?

1 Upvotes

24 comments sorted by

3

u/4eyedbuzzard 3d ago

I’m not electrically inclined and have had zero schooling on the subject.

This makes me somewhat concerned for your safety.

What exactly is fried?
Is it the 480V 3ph contacts, or the 120V contactor coil, both, melted contactor, etc?
Is the contactor rated for the current being drawn by the "heater"? (check heater nameplate and with amprobe)
Contactor for continuous duty heating equipment should be sized at 125% full load current.
Is this just resistance heating element(s) being powered or is there also a motor/blower?
How often does the contactor cycle on and off?
Does it ever chatter?
What controls the energization/deenergization of the coil?

1

u/Mr_Midwest7 3d ago

Heating elements fed directly from the contactor, when it calls for heat contactor pulls in and the output to the elements is adjusted using an SCR. Both contactors are visually fine, but they don’t pull in when given 120v control voltage. The contactor is sized correctly for this application, we use these for other heaters that draw more power through them than the one that I’m working on (same/similar controller just larger elements). No blower being fed from this circuit, that has its own separate circuit fed from the same 420 input, that’s the only place the two interact. The contactor controls the power to the elements, and the control panel sends the 120 signal that tells it to pull in.

1

u/Phreakiture 3d ago

Came back to get it fired up and the contactors weren’t pulling in.

and up to 250v control

Are you sure about the "up to" on that spec? If the contacts aren't pulling in, I'd be questioning whether or not the voltage arriving on the coil is adequate to pull it in.

1

u/Mr_Midwest7 3d ago

According to the data sheet it’s rated for 100…250v

1

u/Phreakiture 3d ago

Okay. That was the first thing that jumped out at me and it seems odd, but if it is on the data sheet, then it's reasonable to expect it to work.

2

u/Accurate-Bullfrog324 3d ago

excellent coaching! constructive, positive, headed to a good result

1

u/erie11973ohio 3d ago

Are the contactors "pulling in" ?

If they are not, then the contactor coils are fried & need replaced. OR there is a control issue.

If the contactors are pulling in & no heat, then the contacts are all burnt to hell & the contacts need cleaned or replaced or the entire contactor needs replaced.


Be careful. 480 will give you a bad day! 😱😱💀💀

1

u/Mr_Midwest7 3d ago

Contactor not pulling in, it’s for sure fried, I just have no idea how or why it got fried

1

u/erie11973ohio 3d ago

Is there voltage at the contactor coils?

No voltage means a control issue.

How old are the contactors??

All thing die with age!

1

u/Mr_Midwest7 3d ago

About a year old, probably less than 200 cycles, and yes I am getting 120 when I should be getting it. I swapped in a test contactor and that pulled in when it was told to every time, so I know it’s getting good voltage

1

u/greenday9261 3d ago

You said the contractor coil is “rated up to 250V”.

Every contractor I’ve worked with has a single coil voltage. If you put 120V to a 208/230V coil the magnetic field will be too weak and not pull in the contacts. This will cause high amperage in the coil which heats it up and kills it.

1

u/Mr_Midwest7 3d ago

Would it be able to pull them in at first?

1

u/greenday9261 3d ago

I wouldn’t think so. I guess my main point in my reply, is just double check that your coil voltage matches your control voltage. Also, sorry for the misspellings in the original post. My phone likes to AutoCorrect contactor to contractor

1

u/bazilbt 3d ago

Heater resistance and amperage of the contactor?

1

u/Mr_Midwest7 3d ago

If anything it’s oversized, we have a similar heater with bigger/more power consuming elements that use the same contactor.

1

u/bazilbt 3d ago

Gotta confirm and confirm it isn't partially shorted. The things that will destroy contactors other than normal wear are high amperage or too many cycles in too short a time.

1

u/jeenyuss90 3d ago

When you say youve got 120v. Is that 120v from a1 to a2?

Have seen it before the neutral is loose. Bringing power to the coil but no return. Most recent case was a knife on a terminal block was open.

1

u/Mr_Midwest7 3d ago

Yes 120 reading from a1 to a2, a1 to neutral terminal, and a1 to ground. I pulled it out of the panel and made a bench test with an old panel whip and a button and gave it straight wall power and it still didn’t pull in. Measured amps and got 0L. It’s definitely fried but I have no idea what did it

1

u/jeenyuss90 3d ago

Does the contactor push in easy when its off?

1

u/Mr_Midwest7 3d ago

Yes

1

u/jeenyuss90 3d ago

Just a burnt out coil. As to why, could just be bad luck if its one. No point chasing a rabbit hole. If it happens again, then theres concern.

If youve got 120v and its stable, just swap it out and move on. If it happens again, you have an issue with the control circuit likely spiking burning the coil out.

1

u/Unique_Acadia_2099 3d ago

It does sound as though the coil is dead and there are lots of possible causes. But one of the main ones is rapid cycling, also called “chattering”. Something in your control system may be causing the contactor to turn on and off rapidly, like multiple times in the span of a few seconds. This will burn the contacts as well, but often will cause the coil to overheat, swell up and jam either open or closed. Jammed closed is an obvious disaster, but jammed open is not. Then if the controls keep trying to close it, the magnetic current stays too high until a coil wire melts inside and current stops flowing.

Control circuit chattering on something controlling heat is sometimes caused by poor design of the circuit, because they fail to include enough “hysteresis” in the command to pull in the contactor. You can’t use a simple thermostat like you might have on a direct control, meaning power goes directly from the t-stat to the elements, like on a baseboard heater, no contactor. Hysteresis means there is a “cut in” (On) and “cut out” (Off) temperature value so that the contactor is not constantly banging on and off. Someone may have not known that, or set to low. This can often happen (in my experience) when a PLC is used and the programmer is unaware of control theory from the mechanical side of things. For example I have seen it happen when they were used to using solid state heating controls like SCRs, then someone tells them to change to contactors because they are cheaper, but they don’t know that the contactor cannot turn on and off as fast as an SCR without damaging itself.

Just something to consider.

1

u/Soft_Garbage7523 3d ago

Coils fail. No particular reason. Some contactors have replaceable coils; others mean it’s a new unit…..

1

u/4eyedbuzzard 3d ago

Replying to update.

Assuming this is an AC output from a PLC or similar:

  1. Is there an R-C snubber in parallel with the coil to prevent damage to the solid state or small relay on the output module when the contactor coil field collapses and creates a voltage spike when deenergized? If so, is it intact? If not present, add one. Size per coil manufacturers specs.
  2. Is the output module rated for the coil current? If not, add a pilot relay.