Apprentice

Post image

Sub 2 hour panel as a 3 month old apprentice. Does it look good to yall or is there anything I could work on? Other than the missing circuit which will have to be pulled and re-ran as the retaining wall they built is too close to the building and there isn’t enough room for the ac units to fit 🤦‍♂️ and ugly labels as I ran out of number stickers. Power comes in from the bottom and for some reason the neutral bus bars were shorter than expected so that’s why everything is about 5 slots down from the top. Have to wait to see what the boss says about that but I’m pretty sure it’s a manufacture defect since all the panels had the same part number and like 4 out of about 20 were like this

13 Upvotes

8 comments sorted by

•

u/AutoModerator 4h ago

ATTENTION! READ THIS NOW!

1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):

- DELETE THIS POST OR YOU WILL BE BANNED. YOU CAN POST ON /r/AskElectricians FREELY

2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:

-YOU WILL BE BANNED. JUST REPORT THE POST.

I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.

8

u/DangitThatHurt 4h ago

Looks good, typically I put all of my larger loads as close to the feeder lugs as possible. So I would have staggered the two pole circuits on the right and the left at the bottom of the panel in your situation. It's just a nitpicky thing. There's no code requirement that drives it. My thought is it keeps the larger loads from having to travel through more busbar than necessary.

1

u/KeyMysterious1845 1h ago

I put all of my larger loads as close to the feeder lugs as possible.

Why ?

2

u/DangitThatHurt 33m ago

Read further in my comment - I explained. To keep the heavier loads closer to the source. You ever seen a burned spot on a bus bar? Have you ever seen an arc welded chunk on a bus bar from a fault in a panel that's still in service? I have seen both several times, in fact on a commercial bolt on panel just last week. I'd rather have my heavier loads be closer to the feeder lugs so as to not further exasperate any potential inconsistencies in the bus before the problem is discovered and repaired. It's simply a precaution, like taping up an outlet in a metal cut in box with hold-its.

1

u/KeyMysterious1845 8m ago

The bus is rated for full MCB.

If theres a failure, it can generally be attributed to a loose connection or faulty bus itself.

Putting larger loads closer to main does noting to mitigate that.

I regularly install oil filled transformers, 128kv breakers, 27kv switchgear, various 480v MCC, etc.

Failures and faults are usually associated with poor workmanship.

A blown bus is going to be replaced, not spit shined with some scotchbrit. The breaker replaced. The conductors megged. The equipment completely checked out.

Your post is opinion and anecdotal.

2

u/cletus72757 4h ago

Nice work kid. 👍

1

u/CovetousCargo03 3h ago

Looks similar to my first panel, one thing I would have done different on mine is try to land wires on top of the panel on the side that the breaker will be, that way the wires cone straight down and don't cross up top. I know sometimes the boss wants it done quick though rather than taking the extra time, and sometimes there isn't a plan for the panel schedule. Looks good though

1

u/ThoopidSqwrl 1h ago

Apprentice also here, looking for a Journeyman to answer. I haven't done really any panel work yet, but shouldn't three be more slack up to for possible future service?