Technical Support Edwards/Kidde CMS input

Hello, I am putting in an Evolve panel (this is the first one of the company) with the VS/FX/VM panels I have not had issues making it communicate properly with the CMS. I have the evolve programmed to send restorations, but it is sending a fire alarm when it comes in and a fire alarm when it restores. Anyone ran into this issue? I've talked to the monitoring and tech support and didn't get around.

0 Upvotes

6 comments sorted by

1

u/Jadedoldman65 8d ago

Is the CMS for this particular install a different one from the CMS's you have reported to in the past? I'm going to throw out one with which I had this problem.

A couple of decades ago (my how time flies) my county of residence set up it's own monitoring station, for city and county facilities. The problem was that the man who programmed it wasn't experienced with programming receivers, and he set up his receiver to act on zone information rather than the qualifier. As a result, dispatch often reacted to restores as if they were alarms. For instance, if the fire alarm system sent an Alarm Activation string "111000000", dispatch received it as an alarm activation. However, when the system sent an Alarm Restore "311000000", dispatch would also interpret it as an alarm activation, as zone "000" was always an alarm.

I programmed mainly EST3 and Quickstart panels back then, so it was easy to give the restores a different reporting zone than the activation.

My suggestions:

First, get a copy of the actual signal the CMS is receiving. (Talking Contact ID). If the qualifiers are correct, it's the CMS programming. If the restores are coming in with an activation qualifier, it's on the panel.

1

u/Damistokles 8d ago

The CMS is the same one I have done FX/VS/VM panels for. It seems to be the way this panel specicially needs to transmit? I am playing the blame game between tech support and CMS it seems. On the CMS report it has 1 is an activation and 0 is restoration which makes no sense.

1

u/JAmBuRriT0 8d ago

What dialer are you using?

1

u/Damistokles 8d ago

Bosch B465 connected to the sadact2

1

u/JAmBuRriT0 8d ago

Ok with the dact2 just make sure you have it set to Evolve and make sure the panel firmware is up to date

1

u/Damistokles 8d ago

Yea, I am getting signals just not the correct ones through. I have the devices imported in but the monitoring service is seeing the restoral and activation of like a pull station as just an activation.