r/firealarms • • 4d ago

Technical Support Simplex technicians HELP

This started on the beginning of the week. I was working on an old 4020. The panel had a trouble for short on the map net card 3, and a communication failure on the same card.

At this point, there was no voltage on the card and I couldn’t even flash the LED because it said it couldn’t communicate with the card.

The card question is a 565 – 368D so we ordered a used one off-line.

At first I installed the new card and every other card also went into communication failure. After messing around with it, be a little and restarting the panel I got to a point where I had the same two troubles as original, however, I was able to flash the LED now.

I also had a random moment where it seemed like it started communicating with devices because a random pull station went into alarm, however I couldn’t even reset that pull after removing it because it no longer seemed to be communicating with the panel. I even attempted to flip other pull stations it did nothing.

Essentially, I had to restart the panel again and get back down to those two troubles I started with.

Obviously, I did check to see if there was actually a short on the field wiring or if voltage would return if the field wiring was removed, but I did not.

A quick sidenote- I did speak to a buddy at JCI and he mentioned this so in case anyone else asks - apparently when he looked up that card, he was trying to tell me it is not the map net Card however like I mentioned, I am able to flash the LED on the map net card and there is no other card it could be.

3 Upvotes

6 comments sorted by

1

u/Snapperhead199 4d ago edited 4d ago

You might have a bad/ wet device dragging down the mapnet channel but not showing up on your meter. Try connecting one device only - straight to the board then power up. Smoke detector or pull station or IAM. If it starts talking, all the other devices will show up as no answer troubles. Then you will have to start breaking the circuit apart to find your trouble. You will need to cycle the power to clear the comm fail /short trouble each time. Check field wire for stray voltage to ground. If it is showing short circuit on power up with no field wire connection, you have a bad board.

1

u/Severe_Celery_4930 3d ago

Wouldn’t all devices be no answer if the loop was just down from a device ?

2

u/Severe_Celery_4930 3d ago

Also the card 3 being in communication failure is that not indicating the card is not communicating or is it saying devices aren’t communicating?

1

u/Snapperhead199 3d ago edited 3d ago

No if the channel is shorted the panel kills all power to the circuit. You have to power down the panel to reset the channel. If on power up it sees a short you will get a short circuit trouble and it kills the power to the mapnet circuit to save the board.

Card 3 comm fail is the panel telling you no devices are talking.

Card 3 missing/ failed means the card is not talking to the master controller.

I was employed by Simplex Time Recorder when the 4020 was introduced. Worked on Simplex stuff for the last 35 years.

1

u/Severe_Celery_4930 3d ago

I’ll go back Monday and test some of this out. I appreciate it. I am an edwards guy so feel free to reach out if you need anything

1

u/TheSpaceman_530 3d ago

Second this. If you've got an analog multimeter handy, I have heard from some old timers that they will actually pick up very slight shorts/grounds better than a digital. Never tried it myself personally.