r/processcontrol • u/S1umL0rdAkr0n • Feb 09 '19
Rslinx does not see device, controller does
Hello all control guru's, I have only been in this line of work for a few years. I do not consider myself a noob (could be mistaken haha) I have googled, reached out to Rockwell tech support and the manufacturer of the device for information and all I have gotten is a "hmm I don't know, I don't think that is our scope". The issue is when I replaced an encoder, RSLinx no longer sees it and places a large red X over the device. When I go into the program in Logix double click on the device in the tree its properties box comes up and it shows running and all is well. I can ping the device if I plug in to the local switch.
First question: Should I even care? Second question: If I should how do i troubleshoot this?
Thanks in advance!
View all comments
Show parent comment
2
u/S1umL0rdAkr0n May 19 '19
Yes, last week we had one of the original integrators come in and I asked him what was going on. He gave me the software from Fraba (the encoder manufacturer) to set the ip address and the subnet mask. When I set up the encoders I used a 255.255.255.0 subnet mask instead of 255.255.0.0, now I can see and access all from RSLinx.