I think it can, im still new to it so I was measuring performance in my iterations by temperature drop between inlet and outlet. Not sure how I can put in a probe for watts exchanged.
On the processor side same thing, you can add wattage in heat on a waterblock and get the temp in vs temp out. I thought I would use this cycle to define ins and outs for each sim
But it was all static and not dynamic so it would take me many cycles to converge
Could you take the temperature difference, multiply by flow in ml/s to get calories/second, them multiply by 4.184 to convert to joules/s which is equivalent to watts?
wow cool! so with a delta t of 5C, flow rate of 120 l/h im getting 690 watts.. whats interesting is that when i run a sim with half the flow rate i get a bigger temperature drop(roughly double), which tells me that the heat exchanged remains constant? that flow rate and temperature difference are inversely proportional. Does that mean it doesnt matter what kind of pump you use? slow fast its all the same? radiator heat exchange capacity is what matters end of the day eh?
I believe two-inlet-at-sides-outlet-at-middle, or two-outlet-at-sides-one-inlet-at-middle, so that the radiator tubes are split in two groups in parallel, could bring down some (non-zero but could be close to zero =P) temps https://i.imgur.com/XVjlZcC.png cuz in theory Q in the second half in series config is a bit smaller due to smaller delta T, I believe it could bring measurable differences.
It does reduce radiator resistance too (by half!) which can thus lower the pump load
14
u/-MadScientist_ Jul 14 '21
This is the full project
9
u/clouddragonplumtree Jul 14 '21
what software are you using to go the simulation?
4
u/maddash1337 Jul 14 '21
That's really handy. Does it also calculate the possible cooling performance. So how many watts can it dissipate?
7
u/annie-adderall Jul 14 '21
Wild. Is that the latest version of Solidworks?
2
u/xvalen214x Sep 16 '21 edited Sep 16 '21
I believe two-inlet-at-sides-outlet-at-middle, or two-outlet-at-sides-one-inlet-at-middle, so that the radiator tubes are split in two groups in parallel, could bring down some (non-zero but could be close to zero =P) temps https://i.imgur.com/XVjlZcC.png cuz in theory Q in the second half in series config is a bit smaller due to smaller delta T, I believe it could bring measurable differences.
It does reduce radiator resistance too (by half!) which can thus lower the pump load
edit: image and Q vs delta E but whatever