r/sysadmin • u/2Fat2MTB • 2d ago
Power Transfer Switch for Single PSU Devices
Good Morning,
I was curious if anyone had a solution for single PSU devices such as modems or the Unifi Agg switch that only have single power sources. I have a full rack with two independent UPS/PDU systems. All of my other gear is either redudant powered via a secondary PSU or my Unifi RPS system.
The only two things that aren't are my Unifi Agg Switch (8 port model) and my Fiber ONT/Modem.
I have a secondary network path in the event my Agg switch goes down due to power loss to all my network switches (blocked normally via STP) but if my primary UPS/PDU system goes down and all my gear falls back to the secondary UPS my internet will not come back up because the fiber is down because it's stuck on the main power source.
I eventually plan on getting a secondary ISP which will been the secondary power (most likely Starlink or 5g) however in the meantime, I'd love some solution to keep at least my Fiber ONT/Modem connected to both power sources so in the event of an outage of one UPS/PDU it will switch and get power from my secondary system.
Would something like this work?
Search Amazon - (AC120V 15 Amp ATS Automatic Transfer Switch,Generator Transfer Switch(NEMA 5-15P/R))
Another problem I'll run into though is my entire system is 208v/240v. I do have a 120v transformer, but that is only connected to one of my UPS systems, so ideally I'd like a transfer switch that I can plug into both my 208v pdu's and connect my single plug devices.
3
u/VA_Network_Nerd Moderator | Infrastructure Architect 2d ago
Is this for your employer environment, or your home network?
3
u/BmanUltima Sysadmin+ MAX Pro 2d ago
APC AP7732 or similar is what you're looking for.
2
u/Weekly-Offer-4172 2d ago
ap7732 is discontinued but the family is still the answer, the current gen is the ap4423 for 230v or ap4424 for 208v (c20 inlets, c13/c19 outlets) and used units land on ebay regularly inside your budget. cyberpower and eaton make rack ats boxes that do the same job too. since it's only one or two devices, for the ont you could skip the ats entirely, it's a 12v wall wart load so a little inline dc ups of the kind sold for routers sits between the brick and the ont and rides through the primary ups dying for way less money. and check the back of your aggregation switch, if it's the usw-aggregation it has a unifi smartpower rps port, a usp-rps powered off the second ups gives it true failover with no transfer switch needed
9
u/IcePick74 2d ago
Eaton PDUMH15ATNET. ATS and Switchbale PDU in one unit.
1
u/ryan8613 2d ago
They exist. What issue are you running into when finding one? I personally use APC/Schneider.
1
u/OtherwiseEffective 2d ago
Not sure what kind of run time you are looking for, but most Fiber ONTs have a special connector to be connected to a dedicated UPS, you could probably also just skip the UPS, and have the ONT be dual feed power, one from the DC barrel jack and one from the UPS connector (just also connected to another DC power supply)
•
u/TrickyAlbatross2802 23h ago
Just checking - what kind of UPS do you have? One note from personal experience, make sure your UPS are dual-conversion "online" UPS's. I've had two "line interactive" UPS's feeding an ATS before, but when there was a power dip, the ATS saw both UPS's down and resulted in a 5 minute outage anyways. The line-interactive UPS just couldn't switch over fast enough to make the ATS happy.
1
u/SVD_NL Jack of All Trades 2d ago
Yeah, automatic transfer switches will work for that, ATS. APC has them, Eaton has them, probably a bunch of others, but i'd personally go with an established brand for this one.
1
u/xubax 1d ago
We've been using APC transfer switches for 10+ years.
•
u/shiranugahotoke 15h ago
I use a Tripp lite ats… but they are not cheap