Bit of a PSA: The technician that did my initial install and the techs that later came to relocate it / repair a bad splice, none of them adhered to applicable code as far as I can tell. They ran the fiber through the crawl space but didn’t secure the fiber cable (NEC 770.24) and when they blew giant holes through the footers and walls, they most definitely did not seal the penetrations with approved fireblock sealant/foam. (NEC 770.26 & to a degree, 300.21)
I don’t plan on selling my house anytime soon but eventually, these code violations could come back to bite me.
Yes, I know about the 2026 NEC reorganization but my state is still adhering to NEC 2017 for single family residential dwellings.
2
u/Hunger-1979 11d ago edited 11d ago
Nobody’s going to care about fire foam or anything related to a fiber install when/if you sell your home…
I work for a fiber ISP in residential capacity and none of us have fiber foam, and we rarely secure lines in crawl spaces.
2
u/Pure-Computer-8317 11d ago
An unsecured cable in a crawl space isn't automatically a violation in every configuration. Its routing, exposure, support, and applicable NEC edition matter.
NEC 770.26 doesn't require every hole drilled through concrete, masonry, or wood to be filled with fire rated foam. Is the penetration passes through a fire resistance rated assembly or compromises required fireblocking?
1
u/Sweendog1107 11d ago
Wtf
0
u/spec360 11d ago
Question is why wasn’t you present ?