I need to install an insulated liner in my chimney, the only one that will fit wrapped is 5.5 inch . My woodstove has a 6 inch connection to it. The chimney is 15.5 feet tall and the stove is an ancient warm morning 520. Will I burn my house down if I downsize a half inch 🤔? Im just trying not to freeze this winter when the power goes out .

Looking at a chimcapcorp 5.5x20 kit and insulating/installing myself .

Is this a terrible idea that I'll regret or what do yall think?

1 Upvotes

3 comments sorted by

1

u/Mopar-or-Nocar 20h ago

Long and short is no don’t decrease the flue. Why don’t need a insulated liner they are a pain in the rear to work with

1

u/TheSilentScoper 20h ago

The exterior of the chimney touches wood, walls and such. Its a 6 3/4 x11inch chimney. A 6 inch would be best but with insulation that turns stuffing 7 inches into a 6 and three quarter space what a nightmare lol. Maybe ovalizing it would work?

1

u/Mopar-or-Nocar 8h ago

Even oval won’t meet the minimum clearance from wood for a liner if it were insulated pipe it would work with the clearance. Insulated liners really suck to work with