Continuity on the wiring is a good start, but an e-stop fault like that usually means the board never sees the input change state, not that a wire is broken. A few things to check:
Watch the input, not the wire. In the input/PLC diagnostic screen, find the input the e-stop is assigned to and press and release the button. If it never toggles, the problem is between the button and the board. If it toggles but the fault stays, it's a config or chain issue.
Check how the input is powered. Many controller boards need the input common wired to a supply (often 24V or the board's own I/O supply) and won't see a plain dry contact on its own. Measure the voltage at the input terminal with the button in and out. It should swing between roughly the supply voltage and zero. No voltage either way usually means a missing common or the wrong sinking/sourcing wiring.
Normally closed vs normally open. E-stops are normally wired NC so a broken wire trips the machine. If the button has NO contacts, or a contact block has come loose from the back of the button (very common on used machines), the logic will be backwards or dead.
Look for other devices in the same loop. On rebuilt machines the e-stop circuit often runs in series through drive fault/ready contacts, a spindle drive fault relay, door switches or a safety relay. One of those being open gives the same fault even when the button itself is fine.
Confirm the input number in the config. If the machine was retrofitted, the wiring may have been moved to a different input than the one the software expects. Compare the wiring diagram, the board labels and the input assignment.
I'd sort out the wiring rather than bypass it. Once the input toggles cleanly in the diagnostic screen, the fault should clear on reset.
1
u/C3p0wn3d 7h ago
There was a loose wire of a common ground! It was the spindle e-stop that was the fault and now we are golden! Thanks folks!
2
u/syil_frans 11h ago
Continuity on the wiring is a good start, but an e-stop fault like that usually means the board never sees the input change state, not that a wire is broken. A few things to check:
I'd sort out the wiring rather than bypass it. Once the input toggles cleanly in the diagnostic screen, the fault should clear on reset.