r/RelayTechs • • Jun 15 '23

r/RelayTechs Lounge

4 Upvotes

A place for members of r/RelayTechs to chat with each other


r/RelayTechs • • 22h ago

Interesting Tripping event.

3 Upvotes

Had an interesting one today. Got 2 dry type 11kv transformers in a building. They are feed of the same CB on level 1. The cable goes from the CB feedera to a old school RMU in the basment with a fuse switch to TX1 then a cable up to level 8 with another fuse switch to TX2.

If we try and energise both TX's at once we go out on Earth Fault..

For saftey reasons we can only energise at the CB amd fuse switches need to be closed whilst de energised.

So we do one at a time. Yep they both hold up on their own.

Ok so heres the kicker. If we Open CB. Close TX2 fuse then close CB, energise TX2. Open CB then close TX1 fuse then Close CB we get an Earth Fault again

If we Open everything. Close TX1 fuse. CLOSE CB. Open CB. Close TX2 fuse, Close CB.... everything holds in....

Bizzare one.

Any ideas.

EF setting is 100amps via Summation. Didnt get TX sizes.


r/RelayTechs • • 2d ago

How do you guys do functional tests during commissioning?

9 Upvotes

We had a substation commissioning job recently and I started to notice that there was a gap in our testing methodology. We had techs NETA-test all the apparatus, yellow-line the schematics, and element test the relays with the canned RTS test plans but it seemed like there was a "Functional" layer of testing that was missing. Some of the issues that we ran into on this project that were not caught by normal testing were:

  • The Trip Coil Fail LEDs on the front of the feeder relays had inverted logic so the LED was ON when the coil was healthy even though the labeled said "COIL FAIL".
  • The breaker failure element was looking at the wrong current input so it would never work.
  • All the CT's on one of the HV breaker were facing the same direction so line differential tripped when they started putting real load through the GSU.

We performed a rudimentary end-to-end test on the line diff but that did not catch the rolled CTs. They guy that tested the CTs didn't catch the polarity issue.

Do your companies have a methodology for developing a "functional" test plan for commissioning jobs. What does that entail?


r/RelayTechs • • 13d ago

School me on Power Line Carrier (PLC) CVTs

Post image
9 Upvotes

Hi everyone.

I’m on a project that has these trench CVTs with the power line carrier module installed inside the junction box, these CVTs are mounted within the yard and not on a line. I have only ever seen PLC once or twice before and the CVT that was to utilize PLC was always outside the yard with a wave trap connected on that line.

What I noticed today while looking at this, the wiring and the phase combining junction box is that it looks like the designer wants to utilize the connections H1 H2 on either side of C3 as a third voltage winding and connect it to a SEL power metering. As I am fairly unfamiliar with CVTs that actually have a PLC module installed I’m not sure if these connections can be utilized as such. I do see the nameplate does reference a voltage here but this might be more for setting the high frequency signal generator up for PLC. I will be reaching out to the designer but figure reddit could possible teach me a thing or two as well.


r/RelayTechs • • 13d ago

Free list of ~500 field relay / testing tech openings from the testing firms' and utilities' own careers pages, updated nightly

24 Upvotes

Looking for testing work usually means checking EPS, Shermco, Qualus, IPS, Vertiv, Saber, RESA, Potomac and the rest one careers page at a time, and a lot of those jobs never make it onto Indeed. So I built relaytechjobs.com. Every night it pulls the field tech openings straight from those firms' careers pages, plus relay and P&C tech jobs at utilities (Duke, PPL, PacifiCorp, Entergy, AEP and more), and puts them in one list.

Right now it has about 500 open roles across 43 states. You can filter by state, by jobs that list pay, and by travel. Each listing links straight to the company's own application page, so you apply with them, not through me. It's free, with nothing to sign up for and no ads. There's an optional weekly email of new jobs in your state if you want it.

https://relaytechjobs.com/?utm_source=reddit-relaytechs

Two questions for this sub:

  1. Which employers am I missing?
  2. If a listing is wrong or stale, tell me and I'll fix it.

r/RelayTechs • • 15d ago

Portable Battery Power Supply Recommendations

4 Upvotes

I've been interested in purchasing a portable battery bank with the intention of using it for relay testing or potentially even low-power apparatus testing (no power factor). Has anyone tried this or found one brand to be particularly suited?

I saw a post on LinkedIn where a guy has his SMRT on the top of his cart and the Milwaukee power station on the bottom and it looked pretty slick. Thanks in advanced.


r/RelayTechs • • 18d ago

Testing a Westinghouse type CA.

Post image
20 Upvotes

Any one have notes on troubleshooting a CA relay. I couldn’t get it to pass the diff unit slope test or the diff timing test.


r/RelayTechs • • 25d ago

25 both not live protection suite test plan help?

4 Upvotes

Im trying to test a both not dead 25 element with protection suite. And with control panel i can get the element to operate by having both line and bus then dropping bus. However i have no clue how to make that test plan in protection suite. Any advice would be appreciated.


r/RelayTechs • • 25d ago

What does everyone else use to connect your 87L channels on 311L relays for testing

Thumbnail
gallery
9 Upvotes

r/RelayTechs • • Oct 21 '26

Interview questions

1 Upvotes

I landed an interview for a relay apprenticeship at a utility, what type of questions did they asked you? What type of questions should I expect? Any tips on how to prepare myself better would be greatly appreciated.


r/RelayTechs • • Oct 15 '26

Power Supply

1 Upvotes

Looking for 24-250v dc power supply options for bench testing relays... good reviewed option out there?


r/RelayTechs • • Oct 08 '26

Electrical testing is harder to explain than people think

Thumbnail
reddit.com
1 Upvotes

r/RelayTechs • • Oct 08 '26

NETA field tech vs. Substation utility tech

Thumbnail reddit.com
1 Upvotes

r/RelayTechs • • Oct 07 '26

Relay tech can mean about 37 different things lol

Post image
2 Upvotes

I recruit in the relay/P&C and electrical testing space, and we just put out an article trying to take some of the mystery out of relay testing.

https://southernstaffinggroup.com/resources/taking-the-mysticism-out-of-relay-testing

Funny timing because I screened a relay tech right after we posted it, and the call reminded me how broad that title can be.

One person says “relay tech” and it could mean SEL, Doble, Manta, Megger, Omicron, end-to-end testing, line carrier work, CT/PT checks, SCADA, commissioning, maintenance, troubleshooting, transmission, distribution, generation, or just getting thrown wherever the utility needs help that week.

That is where I think recruiters can mess it up.

If I only hear “relay testing” and do not ask follow-up questions, I still do not really know what that person does.

For the people actually doing this work, what do you think gets missed the most when recruiters or companies talk about relay/P&C roles?


r/RelayTechs • • Oct 05 '26

Stäubli Test and Measurement Catalog

6 Upvotes

Seen a lot of "where do I buy these" lately. If you have an adapter you can't find or just want to browse, the Staubli catalog is a great reference. Companies can buy straight from them, but I usually just google the part number or look on TME.com for small orders.

https://www.staubli.com/content/dam/ecs/catalogs-brochures/TM/TM-Main-11014124-en.pdf


r/RelayTechs • • Oct 05 '26

Anyone know where to buy these?

Post image
6 Upvotes

I really like these solid wire banana plugs for DC jumpers. I’d love to get some more but I dont know who makes them or where to find them. Any ideas?

Edit: Thanks for all the links! If I cant get my company to buy the Staubli I’ll probably just make some.


r/RelayTechs • • Oct 01 '26

What gets missed when a job posting just says “relay experience”?

0 Upvotes

I recruit relay/P&C roles, and candidates teach me things on calls that I would never get from a job title alone.

I’m learning that “relay experience” leaves a lot unanswered. I want to get better at understanding what someone has actually done and what a position actually needs.

When you read a relay job posting, what details tell you whether it fits your background? And what’s something recruiters tend to lump together that really needs a follow-up question?


r/RelayTechs • • Sep 29 '26

411L Question

7 Upvotes

Does anyone have a work around for testing the 87L before the remote ends are established. I know on the 311’s you can loop back the fiber and use the channel settings to clear the comm alarm and simulate diff but on the 411’s it seems like the loop back only tests the fiber channels it doesn’t allow you too clear the comm failure and simulate diff. I know with TEST 87L in single terminal you can test each phase element but I’m trying to simulate a 3 phase fault. Any ideas would be appreciated


r/RelayTechs • • Sep 28 '26

UK Tech advice

6 Upvotes

Hi I’m based in UK,
Think this is mainly for Americans but wanted to throw out a post -

I’m going into a testing/commissioning role now for a company following being an AP/maintenance tech for a decent sized private network.

Know the basics of VTs/CTs, phasor angles, started reading relay testing handbook by C.W, I’ve mainly worked with Siemens NXAIR with GEs MICOM relays - so gonna be a branch out.

I’m also extremely lacking on the communication side of things as I’ve never worked with PLCs (beyond Uni) and no SCADA.

I know they’re going to give me a SVERKER older model not sure what. And a CMC356
Any good advice, reads or recommendations? Cheers.


r/RelayTechs • • Sep 29 '26

What do recruiters get wrong about relay / electrical testing / field service roles?

Thumbnail reddit.com
0 Upvotes

r/RelayTechs • • Sep 24 '26

Anyone testing mho zones right now? I made a free calculator and need people to try it.

14 Upvotes

I'm a relay tech. I built a mho distance test calculator for SEL relays and I'm looking for people to try it on real jobs.
You put in your settings (Z1MAG/ANG, Z0, CTR/PTR, zone reaches, k0) and it gives you:
The voltages and currents to put on the test set, for any fault type, angle, or % of reach
The mho circles plotted on R-X, with your test point on them
Which bits should pick up, and which zone trips first
A printable angle-sweep test plan
It supports the 311C, 311L, 411L and 421. It's free and there's no signup.
RelayTechs.com
If you're testing zones this week, run a few shots through it and tell me:
Do the numbers match your test set?
Are any setting names wrong for your relay?
What would you want it to do that it doesn't?
Tell me straight if something's off.


r/RelayTechs • • Sep 23 '26

ROCOF Testing with Protection Suite

3 Upvotes

Has anyone here successfully tested a 81R element (ROCOF) using ProtectionSuite?

I'm trying to use the custom macro, but don't really understand the graph of the test shot or what the injected voltage is doing.

Wondering if there are some resources that can help clear things up.

The relay is a SEL-751 that I'm trying to bench test.

Thanks :)

Update: silly me had the wrong phase rotation on my injected voltages. SEL751 defaults for 50/60hz frequency if the phase rotation is wrong. So you don't know it's a problem until you test the relay!

Macros used:

ROCOF: for actual ROCOF

Frequency Ramp with timer: obv for timing

Double Frequency Ramp: for pick up (without tripping)


r/RelayTechs • • Sep 20 '26

How did you get hired?

3 Upvotes

25m struggling to get my foot in the door, finish school next May. Would love if someone would be willing to critique my resume.


r/RelayTechs • • Sep 20 '26

Bunker Hill CC | Electric Power Utility Technology Program

2 Upvotes

Does anyone know how competitive it is to get into this program? / Does anyone know about the program in general? thanks


r/RelayTechs • • Sep 18 '26

NETA vs Relay tech

11 Upvotes

If you had to start over and choose between going through a utility Relay tech apprenticeship or a NETA test tech route what would you choose and what are the pros and cons?

Would a utility Relay tech be able to transition to contracting and vice versa for a NETA test tech?