Interesting Tripping event.

Had an interesting one today. Got 2 dry type 11kv transformers in a building. They are feed of the same CB on level 1. The cable goes from the CB feedera to a old school RMU in the basment with a fuse switch to TX1 then a cable up to level 8 with another fuse switch to TX2.

If we try and energise both TX's at once we go out on Earth Fault..

For saftey reasons we can only energise at the CB amd fuse switches need to be closed whilst de energised.

So we do one at a time. Yep they both hold up on their own.

Ok so heres the kicker. If we Open CB. Close TX2 fuse then close CB, energise TX2. Open CB then close TX1 fuse then Close CB we get an Earth Fault again

If we Open everything. Close TX1 fuse. CLOSE CB. Open CB. Close TX2 fuse, Close CB.... everything holds in....

Bizzare one.

Any ideas.

EF setting is 100amps via Summation. Didnt get TX sizes.

3 Upvotes

15 comments sorted by

4

u/Asheron2 2d ago

Sounds like sympathetic inrush and involving residual magnetization. Analyze the event and see if thats it and maybe have an engineer look into 50P/51P element.

1

u/toolargeforausername 2d ago

I would say inrush.

Are the transformers same group/power/impedance ?

Could you draw a SLD ?

0

u/woodyever 2d ago

The building is 50 years old. They have been running operational. If there was a major difference, it wouldnt hold in at all, regardless of the sequence of energisation

3

u/NeWbAF 2d ago

Maybe in-rush or harmonics.

1

u/aDingDangDoo_Doo 1d ago

That middle 'C' will get you every time.

3

u/fusseli 2d ago

They are delta wyes? What are the chances you have a single CT tapped wrong ratio, that is making fake 3I0 at the relay

2

u/Itchy_Crack 1d ago

Ground faults are gonna be read symmetrical as a zero sequence fault.

Almost certainly some form of an imbalanced inrush. Depending on the relays I'd see if the voltage collapsing during the inrush appears as a fault.

-1

u/Fideli91 2d ago

Are you saying that the two transformers are in series with each other? Or are they parallel off of a bus?

2

u/woodyever 2d ago

Parallel of the same bus

0

u/Fideli91 2d ago

Ah ok thanks. I’ll have to ponder this one

0

u/Fideli91 2d ago

Do they hold in if you open everything, close both fuses and then close the CB?

1

u/woodyever 2d ago

Negative. Have to close fuse 1 first then turn off and close fuse 2 next for them to hold in. Both at once oe tx 2 first cause trip

0

u/Fideli91 2d ago

What type of relay is doing the tripping? And is this a 3 phase system?

1

u/woodyever 2d ago

Yes 3 phase. Its a ABB REF615. I couldnt connect to get the COMTRADE file wr jus had to get power back on

1

u/Accomplished-Cap3252 2d ago

My priority would be getting the waveforms of the trip, and also the successful energization if possible (now that power is on).