r/hvacadvice • • 6h ago

Pros: what should a homeowner check before calling you for a no-heat call?

0 Upvotes

Cold week coming for a lot of people. For the techs here: what are the few things a homeowner can safely check first (thermostat, filter, breaker?), and what should they never touch and just call you for?

Hoping this saves someone a service fee and keeps people safe.


r/hvacadvice • • 1h ago

Roofers damaged exhaust flue

Post image
3 Upvotes

Everyone is safe now, but I'm wondering how this situation should have been handled.

I recently purchased a duplex, and funds were escrowed to replace the roof as part of the deal. The roofing company was contracted by the seller.

I did an in-person walkthrough shortly after the roof was replaced, and the photo shows how I found the exhaust flue from the gas furnace. Unless I'm mistaken, it was a really dangerous situation that could have lead to carbon monoxide leaking into the living space. It was apparent to me that the roofers miscut or slid the decking down the slope, which pulled the flue apart like this. When I tried to move it back into place, the penetration in the roof was misaligned and the duct could not be straightened.

After shutting down the unit, I called the roofing PM, who initially denied that they had anything to do with the situation. After a brief discussion, he agreed to send the workmen back to attempt a fix. Ultimately, I wasn't satisfied because their fix did not result in a straight duct and involved quite a bit of foil tape.

Afterwards I sent my HVAC guy to inspect, and he was able to salvage the setup and sign off on it after doing a CO test.

How would you have handled this? I didn't exactly hire the roofers, and although I'm certain they did the damage, they didn't necessarily have the skills to repair it. I'm going to let the roofing company know what happened in hopes they won't have a crew that does that again. I also don't think the PM probably told his bosses.


r/hvacadvice • • 7h ago

Replace blower ASAP?

Thumbnail
gallery
1 Upvotes

Looking for a second opinion on the condition of this blower inducer. Was advised to replace ASAP, said he doesn't see them this bad very often. Still works, seems pretty quiet IMO. Hopefully the pictures are useful.

**Edit** Was told it was leaking.


r/hvacadvice • • 11h ago

NEED HELP !!

0 Upvotes

We have been dealing with some sort of feeling of being light-headed waking up groggy but we feel fine when we leave the house but once we come back in we feel the same way I ordered an air tester monitor and notice we get high levels of CO2 any idea what it could be! And this is with the windows and air conditioner on and everything aired out I notice its very high when we run appliances or in the kitchen


r/hvacadvice • • 5h ago

Running duct above non-structural wall?

Thumbnail
gallery
14 Upvotes

I'm building out a soft story into livable space. We have a big I-beam above this wall that separates rooms, and need to run ducts somewhere. I'd like to avoid a soffit and came up with this idea to shorted the stud wall and run the duct along the top of it.

Is this dumb?


r/hvacadvice • • 18h ago

No heat Furnace died 3 months after buying the house. One company says $3.3K repair, two others says full $30-35K replacement. Looking for advice/opinions for a first time homeowner.

Thumbnail
gallery
10 Upvotes

Bought a house in Tomball, TX (Houston area) in August 2026. The inspection report didn't flag anything about the HVAC. On 11/16 I woke up with no heat. System is 12 years old, zoned, single-stage equipment.

What the first tech found
Gas valve leaking gas into the system
Hot surface igniter reading 58 ohms
Zone control board not sending a proper 24V signal
His claim: the existing single-stage equipment isn't compatible with zoning (static pressure problems), so the system was improperly installed.

Quotes
Repair only (igniter, gas valve/pipe/sediment trap, zone board): about $3,300
Full 4-ton Daikin Fit zoned replacement: about $29,000 from one company, about $35,600 from another

Other context
Home warranty claim was denied, with the reason given as improper maintenance by the previous owner. I'm appealing. A neighbor told me the sellers had HVAC people out 5 or 6 times around closing, so I suspect issues were known before the sale.

My questions
Is a full replacement really necessary, or is it reasonable to repair now and revisit later?

Is a variable-speed inverter system like the Daikin Fit worth the premium over a standard two-stage system in this climate?

Is the "single-stage equipment can't be zoned" claim legitimate, or could that be an upsell?
Is a $6K gap between two quotes for the same equipment normal? What should I ask each company to itemize?

Anything I should have a third HVAC tech check or photograph before anything is removed?Happy to share model numbers and photos if that helps.

Thanks in advance!!!


r/hvacadvice • • 2h ago

Hanging a modine hot dawg 100k

Thumbnail
gallery
3 Upvotes

Looking for input on hanging i went the 3/8 threaded rod and unistrut route since I have 14' ceilings and wanted it mounted at 9.5' . How ever not confident with the swaying it has. Is this the right path and do I need some sort of bracing and if so how thanks.


r/hvacadvice • • 2h ago

Furnace Struggling

1 Upvotes

Is anyone able to help me diagnose this to try to diy before I spend hundreds on a service call?

Almost every time my furnace goes to kick on, it repeatedly does this rhythmic knocking and locks itself out for a few minutes. I usually have my house set to 22°c but with this going on it never reaches temp and continuously cycles through this problem.

The igniter seems fine, the gas comes out evenly and cleanly, but when (I believe) the blower tries to turn on it just locks out


r/hvacadvice • • 7h ago

AC Clogged AC Drain

Thumbnail
gallery
1 Upvotes

Every 1-2 months my AC will stop turning on until I drain this pipe with my Shop Vac. I used to pay $40-$60 to have a guy come out and shoot the gunk out from the attic. They never gave me a reason why this happens just said “it’s normal maintenance” Is there any way to stop this from happening? Is the pipe too small?


r/hvacadvice • • 7h ago

Boiler Hydronic check valve vent leak

Thumbnail
gallery
1 Upvotes

I had to replace my main water pressure regulator the other day. This released a slurry of crud that percolated through my system, clogging stop valves and supply lines. Apparently it also jammed up the check valve for my boiler. This was installed in 2023 so it looks pretty clean otherwise.

I've owned this house for only 3 months. This is a new leak that happened since the regulator swap. If I close the valves adjacent to this it looks like I can pull it and clean or replace with a minimum of water loss.

I have limited experience with baseboard hydronics, but am very familiar with in-floor radiant. Can I count on the spirovent to take care of trapped air after this work or will I need to take other steps?


r/hvacadvice • • 8h ago

Furnace Green residue, copper corrosion?

Post image
1 Upvotes

I’ve reached out to a local HVAC company and am waiting to hear back. A lot of what I’m reading online says the green is a clogged condensate line, but I was able to flush mine and it appears to be flowing freely. Does this appear to be more f a copper pipe corroding? Thank you.


r/hvacadvice • • 1h ago

Quotes AI is telling me that the contractor's estimate is too high for replacing capacitors in a commercial building. I've no idea how much these things should cost -- should I get a second quote ?

0 Upvotes

*thank you everyone that replied! I got my answer! will get a second quote from another hvac company*

The technician found genuine wear-and-tear items that are worth addressing before they cause a breakdown, but the $1,085.54 quote is heavily inflated. You are being charged full standalone "flat-rate" prices for four inexpensive parts ($15–$30 each) that can all be swapped in a single 30- to 45-minute visit.

More importantly, the technician noted leaking refrigerant valves—which is a bigger threat to your systems than the electrical parts—yet didn't include them on the quote.

What the Report Means in Plain English

1. The 3 Run Capacitors ($770.67 quoted)

A capacitor is a small metal cylinder that stores and releases a steady jolt of electricity to help your blower motors and compressor start up and run smoothly. Its strength is measured in mfd.

Over time, capacitors weaken. When capacitance drops too low, the motor has to pull higher amperage to compensate, which makes it run hotter and shortens its lifespan. Replacing weak capacitors proactively is smart—they are cheap insurance for expensive motors.

2. The 2-Pole Contactor ($314.87 quoted)

A contactor is a heavy-duty electrical switch (relay) that clicks closed to send high-voltage power to your unit when the thermostat calls for heating or cooling. The technician noted a "lowish-ohm reading" on the package unit's contactor coil, which indicates the internal electromagnetic coil is starting to degrade. If it fails, it can either stop clicking closed (no heat/AC) or weld itself shut (running the compressor nonstop until it burns out).

3. Schrader Core Valve Leaks (Missing from the quote)

Schrader cores are the tiny internal valves inside your refrigerant service ports—identical to the valve inside a car or bicycle tire. The tech noted 3 out of 5 were loose/leaking, with "leak and seal" (a refrigerant stop-leak additive) dripping out of one. This is a priority: if refrigerant slowly leaks out, your system will lose heating/cooling capacity and eventually damage the compressor.

4. Return Air Note (Missing from the quote)

"Mechanical room not pulling return air from either floors" suggests either a damper is closed, a return duct is disconnected, or the unit is pulling air straight from the mechanical room instead of circulating air from your floors. Ask the tech to clarify what they observed here.

Price Check: Why It Costs Over $1,000

Most HVAC companies use flat-rate pricing, where each line item bakes in the part, technician labor, truck overhead, and warranty. When a company stacks four flat-rate items on one invoice without a multi-part discount, you end up paying for four separate service calls in a single visit.

Quoted ItemQuoted PriceActual Part CostTypical Labor Time
Dual run capacitor (20–50 mfd)$271.67$15 – $2510 minutes
Single run capacitor (blower #1)$249.50$10 – $2010 minutes
Single run capacitor (blower #2)$249.50$10 – $2010 minutes
30/40A 2-pole contactor$314.87$15 – $3015 minutes
Total$1,085.54$50 – $95~45 minutes

Even with a healthy commercial markup and a full hour of labor, a fair bundled price for all four parts installed during one trip is typically $450 to $650.

What to Ask Before Approving Anything

  1. Ask for the exact test readings. Capacitors have a tolerance of ±5% to ±6% (for example, a 45 mfd capacitor is fine down to ~42 mfd). Ask what the actual mfd readings were on each capacitor—if they are only slightly out of spec, they are not an emergency.
  2. Ask for a bundled multi-part discount. Tell them you want to get all four parts done at once, but since the technician is already on-site with the panels open, ask if they can bundle the labor rather than charging four separate flat rates.
  3. Clarify the Schrader valves. Ask if the tech already tightened and stopped the leaks during the maintenance visit, or if the cores need to be replaced (a $5 part that takes minutes with a core removal tool).
  4. Get a second quote if they won't budge. Any licensed independent HVAC technician can swap three capacitors, a contactor, and tighten/replace Schrader cores in under an hour for roughly half of this estimate.

r/hvacadvice • • 4h ago

HVAC installer wage

3 Upvotes

i started at 21$ an hour 4 months ago i got a raise of 24$ is that too little? this is CA norcal


r/hvacadvice • • 2h ago

Contractor accidentally cut mini split wire

Post image
23 Upvotes

Can anyone tell me how serious this is? And is it capable to splice back together? Thanks in advance


r/hvacadvice • • 22h ago

Furnace Any idea what this white chalky like powder is on our furnace?

Thumbnail
gallery
15 Upvotes

I couldn’t tell you how long it’s been there, maybe a couple months max. I only go down to our furnace room to change the filters and didn’t see it 90 days ago. Our furnace is 15 years old and we have been running our heat now for a few weeks. It’s a chalk like powder.


r/hvacadvice • • 2h ago

Are my B2B lead generation prices reasonable?

0 Upvotes

Hey everyone

I'm starting a B2B lead generation service targeting HVAC companies.

My packages:

- One-time: 30–40 leads for $500–$750.

- Monthly: 80–100 leads for $1,500–$2,000.

Leads include researched companies and relevant contact information.

Are these prices reasonable? Would HVAC companies pay for this service?

Honest feedback appreciated.


r/hvacadvice • • 22h ago

Water Heater Venting

Thumbnail
gallery
9 Upvotes

A friend of mine asked me to flush his water heater today. I am a 40yr tech. As we were talking while it was draining i noticed the venting on his water heater.
I advised him that it is deadly. He said he cant afford to replace it. I told him he cant afford not to.
As you can see, it travels downhill into a tee, with the furnace, then horizontally to chimney.
This passed a home inspection last year!


r/hvacadvice • • 22h ago

Water Heater Venting

Thumbnail
gallery
152 Upvotes

A friend of mine asked me to flush his water heater today. I am a 40yr tech. As we were talking while it was draining i noticed the venting on his water heater.
I advised him that it is deadly. He said he cant afford to replace it. I told him he cant afford not to.
As you can see, it travels downhill into a tee, with the furnace, then horizontally to chimney.
This passed a home inspection last year!


r/hvacadvice • • 44m ago

Furnace Sanity Check...Tune-up turned into $3,600 in quotes on a working 2017 furnace

Thumbnail
gallery
4 Upvotes

**Edited for completeness. Including the readings and estimates in the message body that didn't get submitted the first time**

Hey everyone,

I requested a tune-up on my 2017 2-stage gas furnace (F9MVE0801716A3) in Southwest Ohio. I didn't see any symptoms, holding 70°F fine. I wasn't home for the tune up and my wife wasn't very helpful explaining why the tech left us with three estimates totaling ~$3,600. I'd appreciate a quick sanity check on whether anything here is actually urgent and if it is reasonable.

Tech's readings:

Delta T: 35°F on low fire / 53°F on high fire (rating plate specifies 30–60°F / 40–70°F)

Manifold gas pressure: 1.8" WC low fire / 3.4" WC high fire (specification is 1.3–1.7 / 3.2–3.8)

Flue CO: Approximately 64 ppm (not sure whether raw or air-free)

Flame sensor: 1.1 µA before cleaning, 1.7 µA afterward

Indoor humidity: Approximately 47% RH, although the Fieldpiece screenshots appear to have the probes mislabeled/swapped

Recommendations/estimates:

$849 – Ignition repair: Replace flame sensor and hot-surface igniter and clean burners. The technician described the burners as heavily rusted and the igniter as having heat-stress marks, although it reportedly tested within range. I wasn't provided a photo of the igniter.

$1,149 – UV air purification system: Replace the existing UV system because it's no longer working. I have a spare bulb that I haven't tested yet.

$1,600 – AprilAire fan-powered humidifier: Recommended because indoor humidity reportedly drops to 37–40% during winter. We currently measure around 47% RH and haven't noticed any dryness.

Quotes:
Would you consider any of these repairs urgent based on the information/photos? I guess specifically, should the heat exchanger rust or burner condition be looked into further, or does this look more like preventative recommendations and optional upgrades? Would you get a second opinion before approving the ignition repair?


r/hvacadvice • • 45m ago

Boiler What do you use to clean these heat exchangers?

Post image
2 Upvotes

r/hvacadvice • • 1h ago

Furnace HVAC blocking attic access

Thumbnail
gallery
4 Upvotes

I just bought a new home, and I think I might have a roof leak in my bathroom after some rain this past week. I noticed some water leaking out of a wall mounted light fixture in the bathroom.

I’m not a handy person, but I wanted to take a look at how things looked in the attic space above that bathroom.

I popped my head in the attic, and I’m seeing that my HVAC unit is completely blocking access to the part of the attic that I need to get to. There doesn’t seem to be any clearance for me to climb over or around the HVAC unit.

Does anyone have any advice for how I can move past or over my HVAC unit?

Or is there something I can take apart from the HVAC to give me some clearance, and then reattach once I’m done looking? I wasn’t sure if I might be able to safely unscrew/untape the big duct in my 2nd picture


r/hvacadvice • • 1h ago

Am I getting honest an assessment and price quote?

Post image
2 Upvotes

Recently bought a home and had someone come out to get the heater started (it is So Cal, it takes a while to get our version of cold) and I as told I would need a new blower motor as the pic he said indicates a gas leak and can be dangerous.

He also said the orange flames in the video indicate the heat exchange is on its last legs and needs replacing. He showed me a pic with a bunch of small holes in it. I am being quoted around $6500 for parts and labor, plus being offered another $1500 in cleaning our ducts and stuff.

What do you think?


r/hvacadvice • • 1h ago

Looking for replacement gas valve

Thumbnail
gallery
2 Upvotes

The pilot does not stay on, I replaced the thermocouple, and verified I'm getting about 28mV from the thermocouple.

I think the safety valve in the gas valve is bad, so looking to replace the valve. It's a very old unit so I can't find a direct replacement. Can anyone tell me if a newer model of gas valve will safely work for this unit? If so how do I determine what I type/model of valve I need to buy?

It's natural gas with a thermostat built into the valve


r/hvacadvice • • 1h ago

Need advice on tools to buy for new technician

2 Upvotes

My partner is currently in school for HVAC and he’ll be certified next summer. I want to get him some tools for Christmas but I honestly have no idea what to get. What would you consider to be the most important tools to have going into the trade or what should he absolutely have to start with?

He’s got a good basic set of everyday tools from home and car repairs but nothing crazy. Would love to stay under $100-$150 since it wouldn’t be his only gift. Any advice or suggestions are much appreciated!